Hi All

Just doing some planning.
What is typically done for power cable from the windmill to whatever interface you guys use, and do you normally run 3 phase AC down the pole and rectify it at the ground, or rectify it on the windmill and run DC down the pole?

I found a good youtube clip which has an attached excel sheet for doing calculations which is quite useful.

https://www.youtube.com/watch?v=uS7CyTxAA4o

Based on this, my estimation whether I run AC or DC down the pole, I am in the region of requiring AWG 8 cable, which isnt cheap stuff.
My estimation so far is 15m one way, so 30m of cable (assuming DC 2 wire).

Curious what others are using and where you sourced the cable from.

Thanks
 
BarkyJ
Senior Member

Joined: 26/04/2018
Location: New Zealand
Posts: 114
Posted: 01:40am 11 May 2018
Copy link to clipboard 
Print this post

http://www.nzev.co.nz/10mm-flexible-cable/

This is what I am currently looking at.
 
Warpspeed
Guru

Joined: 09/08/2007
Location: Australia
Posts: 4406
Posted: 12:42am 12 May 2018
Copy link to clipboard 
Print this post

You do not say what your system voltage is, or the expected current.

Ten mm squared cable has a resistance of .00172 ohms per linear meter, so 30m of that cable will have a resistance of .0516 ohms (at 20 Celsius).

The "normal" current rating for 10mm cable is 50 amps.
I squared R gives a power loss of 129 watts at 50 amps for 30m of cable.
Voltage drop at 50 amps would be 2.58 volts.

I have no idea if those are significant figures for your intended application.
Cheers,  Tony.
 
BarkyJ
Senior Member

Joined: 26/04/2018
Location: New Zealand
Posts: 114
Posted: 05:03am 12 May 2018
Copy link to clipboard 
Print this post

Sorry the system voltage at this stage is 36V.
 
Warpspeed
Guru

Joined: 09/08/2007
Location: Australia
Posts: 4406
Posted: 06:16am 12 May 2018
Copy link to clipboard 
Print this post

So its going to have about 7% loss at 50 amps.
Cheers,  Tony.
 