I'm building a charge controller based on the one found on this site:
http://www.mdpub.com/Wind_Turbine/. I've made a few minor changes and
am considering another but I'm not sure how to accomplish it. This is a
shunt controller so if the batteries get full it redirects the incoming
current to a dummy load. What I'm considering doing is seeing if I can
add to the circuit so the circuit can tell if there is nothing connected
on the dummy load output and if so have it instead short the inputs (I'd
probably include a button to purposefully short the input as well for
braking). My thinking is that while shorting the input is not the
preferred method it is better than having the circuit try to dump to the
dummy load and have nothing there, allowing the turbine to freewheel.
This would allow for hooking the controller up without a dummy load in
the right circumstances or just be a protection in case the dummy load
was either not hooked up properly or experienced some type of failure.

My first question is, are there any arguments about this being a bad
idea?

Next, I'm just learning electronics so don't really have the expertise
to design this new portion of the circuit myself. Anyone have any ideas
or reference links they can provide for something that could do this (if
resistance equals zero then trip this relay)?

My last question is how can I determine what the capacity rating for
this controller would run? Is that solely based on the Diodes, Fuses,
and circuit (trace or wire) capacity? The circuit for the charge
controlling itself has only a low amount of power going through it so
I'm just guessing it is the rest of the components that would dictate
the current capacity of the entire product.

Direct information or links to pertinent online materials welcome.

Thanks all,
Brian in Oregon


-Brian V
Hillsboro, OR (USA)
KF7DUZ
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 12:07am 12 May 2010
Copy link to clipboard 
Print this post

Hi Brian

Have a look at Gizmo's Charge controller here... http://www.thebackshed.com/windmill/articles/TL084-Controlle r.asp

As it will do the monitoring you wish for the dump load.
What you would do is set it to cut in a little bit higher than the existing controller.
So if there is no dump connected or you have a faliure the voltage will rise above where the normal dump would cut in, and be sensed by the 2nd controller and switched to what ever you choose to connect to the relay..Short or 2nd dump, etc.

Pete.
Sometimes it just works
 
Pukwudji
Newbie

Joined: 10/07/2009
Location: United States
Posts: 20
Posted: 01:49pm 12 May 2010
Copy link to clipboard 
Print this post

That seems awfully complicated. Can I not simply use some type of gate to detect when there is no resistance on a circuit and use that gate to trip a relay?

I was thinking I could feed low voltage to the dump circuit and compare the voltage coming out the other side to an extremely low voltage (<1v) from my main circuit (through diode to prevent power going back down this part of the circuit if the dummy is actually present and power is dumped to it). If the dump circuit voltage is lower than this feed (like 0) I could then trip a dpdt relay which would short my + and - source leads together. I still have two gates on a quad OpAmp and two gates on a quad NOR gate in my main circuit that aren't doing anything right now.

I could very likely be wrong and oversimplifying this as I'm still pretty new, but I'd hope to add this function without doubling the size of my current circuit.

Thanks,
Brian
-Brian V
Hillsboro, OR (USA)
KF7DUZ
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 02:54pm 12 May 2010
Copy link to clipboard 
Print this post

Ok i didnt look at the circuit before and just had a quick look now.

The circuit shows a dual opamp not a quad so i guess you have changed this.

Yes you could fudge something like you surgest and even get away with only the 2 remaining NOR gates but i see it a problematic method that might not be reliable.

As the controller is the last line of defence between overcharging and or destruction i would want more reliable proven method.

SO if you do have 1/2 the opamp spare and 1/2 the NOR gate spare than why not just double the present circuit as its only a few resistors and a pair of trimpots, then set one circuit slightly higher than the other, that way the higher one should never activate unless you have a problem with the main circuit. ( being the lower set one)

The same Vreg will do both circuits.

It is the battery voltage you really need to monitor and dont give a dam about the dump load.

You could even set it up so the mill shorting relay was held closed for normal operation and was unlatched by the 2nd circuit, this way if power was lost to the system at any stage the relay would dropout and inturn short the mill.
A fail safe method.
This is used by some other members here on larger AXFX mills, but it do mean the relay is always drawing power.

Pete.
Sometimes it just works
 