Chrismar
Newbie
Newbie


Joined: 27 May 2015
Location: United Kingdom
Online Status: Offline
Posts: 3
Posted: 11 March 2016 at 9:20am | IP Logged Quote Chrismar

Hi

I am in the process of building a windmill generator using a F & P smart drive, I have rewired to a 6 wire star & delta config. I now need to hook up to an automatic / programmable switch that will switch between the star & delta. I took this from the [URL=http://www.yourgreendream.com/diy_fp_rewire2.php] site that explains a bit further what I am after. Any help as to what I can used and where I can purchase?

Also has anyone got any advice on a controller and how to wire / configure to drive a factory configured smartdrive as a motor (NOT GENERATOR).

Any help and guidance will be appreciated

Chrismar


Back to Top View Chrismar's Profile Search for other posts by Chrismar
 
Downwind
Guru
Guru
Avatar

Joined: 09 September 2009
Location: Australia
Online Status: Offline
Posts: 2332
Posted: 11 March 2016 at 11:31am | IP Logged Quote Downwind

Switching between star / delta has been a age old debate, personally I see it a danger area, as all electronics are subject to fail at some point, and from someone who have designed and built more electronic circuits in this area than most here I would not go the path of star delta switching.

The rule of thumb to any windmill control design is "fail safe" and a switching system has no way of fail safe.

What ever you do and how ever you do it the mill must always be connected to a load at all times, and switching allows for a runaway mill should switching fail.

really star delta switching is only required if you got the mill winding totally wrong to start with and is simply a bandaid for a poor mill design.

Should you be building a VAWT, than little to add other than a very poor choice of mill and nothing will fix the low output even with fancy electronics.

Pete.

__________________
Sometimes it just works
Back to Top View Downwind's Profile Search for other posts by Downwind
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 12 March 2016 at 10:10pm | IP Logged Quote DaveP68

Hi Chrismar

Electronic Switching is best done with delta wiring from my experiments.

The idea is to say cut a 36 pole stator into quarter or sixth depending on how much switching is required over a wide RPM range.

Each delta set of winding's is terminated into it's own rectifier which can then be switched using FET's to put all outputs in series or parallel depending on RPM at the time of the switching for a given voltage output.

Example;
At 100 RPM with a 36 pole stator 4x delta winding's all in series would produce 50V, .62A, 31W
At 200 RPM with same stator 2 sets of 2x in series put in parallel would produce 50V, 2.42A, 121W
At 450 RPM with same stator all delta winding's in parallel would produce 50V, 9A, 450W

Note the big jump in current range, this is due to the load better matching the stator so it's not going into saturation.

The FET's need to be fast switching and very low on resistance, with a make before break switch over so stator doesn't see an open circuit condition.

The switching can be done at different RPM's to produce lower or higher voltage.

The 36 pole stator is the best to use with a black rotor cap as stronger magnets. Also it can be cut into more configurations 1x 12, 2x 6, 3x 4, 4x 3, 6x 2 allowing a wider range of switching points. The stator can also be used in star mode for higher output voltage but less current. Difference is 1.732 times so delta volts 200 RPM uncut 100V 1.21A vs star 173.2V 0.7A same RPM.

I prefer delta wiring as better current output for Voltage I'm wanting at a given RPM.

What do you think?

Cheers

David
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 15 April 2016 at 9:09am | IP Logged Quote DaveP68

Here is a table of that proves my point that the power output of these F&P stators must be managed through a switch system or DC to DC converter (advanced charge controller).

The power outputs in the table is from a 36 pole Stator wired in Delta mode uncut and using a Black rotor cap into a 86 ohm load.

The 1/2 cut plus 1/3 cut results in the table are scaled. I have already proven the scaling dose work from other testing just didn't want to repeat the same RPM tests another 2 times.

RPM Watts Volts Amps Volts 1/2 Amps 1/2 Volts 1/3 Amps 1/3
60___12.5__33__0.38__16.5______0.76_____11.00_____1.14
100__32.2__52__0.62__26.0______1.24_____17.33_____1.86
120__46.5__62__0.75__31.0______1.50_____20.67_____2.25
150__69.9__76__0.92__38.0______1.84_____25.33_____2.76
180__94.5__90__1.05__45.0______2.10_____30.00_____3.15
200__121__100__1.21__50.0______2.42_____33.33_____3.63
250__178__123__1.45__61.5______2.90_____41.00_____4.35
300__245__144__1.70__72.0______3.40_____48.00_____5.10
350__311__162__1.92__81.0______3.84_____54.00_____5.76
400__384__183__2.10__91.5______4.20_____61.00_____6.30
450__454__200__2.27__100.0_____4.54_____66.67_____6.81
500__527__215__2.45__107.5_____4.90_____71.67_____7.35
550__585__225__2.60__112.5_____5.20_____75.00_____7.80
588__660__240__2.75__120.0_____5.50_____80.00_____8.25
800__880__275__3.20__137.5_____6.40_____91.67_____9.60

The maximum output 880W was due to me using a 1200W drill with which resulted in that being the maximum shaft power it could produce.

The 86 ohm load is the optimum load for this stator uncut in delta mode. Any deviation from this load to a higher or lower resistance will result in a lower output power. You will now see why it isn't practicle to connect them directly to a battery without using a DC-DC converter or some form of switching system at cutting in at different RPM ranges.

Hope this data is of use to you and others that would like to use it.
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 15 August 2016 at 10:58am | IP Logged Quote DaveP68

For those interested that are not sure how to interpret the table above, I've made a graph from that same data showing it's optimum operating output. As stated above I used a 36 pole stator wired in Delta mode uncut with a black rotor cap into a 86 ohm load.

Horizontal axis is RPM.



The steeper the rise in operating output power vs RPM the less efficient the stator will operate.

Will upload further graphs to prove my point once I created some new data tables with loads which are too low or too high resistance for the stator to remain efficient.
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
fillm
Guru
Guru
Avatar

Joined: 10 February 2007
Location: Australia
Online Status: Offline
Posts: 718
Posted: 17 August 2016 at 11:28am | IP Logged Quote fillm

Hi Dave,
I can not really see the point of giving output data into loads that do not represent anything that is useful like energy storage / battery charging or a grid tie and then secondly to get to the higher output the RPM is in a range where a wind turbine rarely operates at unless its in Antarctica. You might have some kind of controller I have not heard of to turn that data into something.
The voltage range of 16 to 137.5V is such a wide range and you have not given a purpose other than 86Ohm is the best load. Testing and posting data is great but what is normally an 86 ohm load and has a purpose. Also setting up Star delta switching ect to maintain maximum output at RPMs that can only be achieved in 40+ KLM wind is messy and doomed.
Dont get me wrong , I think the F&P is a great thing and is one of the few PMAs can be smashed by 100klm winds all day and not burn out and if it strong enough to take the battering.
We did a lot of testing a few years back and I cut my turbine teeth on the F&P and to date have not seen or come across a black rotor. But if the windings are not .8 or 1mm then I would think the output would be limited in real world testing and if it gets over 400W I would be surprised

Below is probably a bit of a plug but of no use here as 99.9% of the audience and members here are not the buy it ready to go type and more build it DIY. Also watching for new posts in the wind section here is at an all time low so please don't be discouraged
Anyway what the latest 1kW - 2.5kW OZ Wind Turbines can output into a 48V / 24V battery and all at under 400Rpm with no Epoxy.
The logging screen is for a 2.5kW has been collaged as only 1 peak can be shown at a time but these are absolutely one of the best Alternators. Everything is kept at very low RPMs and in control and coupled with the unbelievable torque of the GOE222 Airfoil it makes them the a very high performance turbine. In 20 - 25klm it is just ticking over at 1kW into the batteries.



__________________
PhillM ...Oz Wind Engineering..Wind Turbine Kits 500W - 5000W ~ F&P Dual Kits ~ GOE222Blades- Voltage Control Parts ------- Tower kits
Back to Top View fillm's Profile Search for other posts by fillm Visit fillm's Homepage
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 18 August 2016 at 12:16am | IP Logged Quote DaveP68

Hi Phill

I think you may have over looked some points made further back in this post.

For starters I work with these Fisher & Paykel washing machines as a job and know how they work down to a component level in the motor controllers and motor operation. So understand PWM theory etc.

The data you see is what I got from a single 36 pole copper stator wired in Delta using the new version Black rotor cap.

See photos of test set up (instrumentation not in photos).





The back rotor cap you can see in the lower photo have been used on F&P machines built in the last 7 years, so not many been scarped. This may explain why haven't seen a black rotor cap yet.

My point with doing testing into an 86 ohm load (in same photo to right of black cap) is that it's the most efficient load match over a given RPM range. I'm not saying the FET switching system is a good idea under extreme conditions.

If the goal is to have power storage into say a 48V battery system, a direct connection via a charge controller is why 400W is the max output for a single stator.

If say a form a buck converter is used so output of the stator is allowed to operate over a wide voltage range. The converters output can thus be 56V if that is the best float voltage for the batteries.

The minimum converter input voltage range being a least 3 to 1 allowing current to do it what it does best under MPPT control. A 10 to 1 being ideal which really ever achieved. If you can get 4 to or even 5 to 1 even better efficiency will be achieved.

So the resistor load test was only to prove the best load conditions with max a of 275V at 3.2A DC 880W output measured into that 86 Ohm load.

These 36 pole stators can be cut into more combinations than a 42 pole. I.e. 1/2, 1/3, 1/4 or 1/6 cuts, if one want to take a risky switching system on. Not advised from what you know...

I'm not disputing that you chaps have done lots hard work and achieve good results over the years as I'm still new to this.

Like I trying to state here is these F&P stator are only designed to see a constant load "like a resistor" to give their optimum output.

Fred (flc1) who I'm in touch with on ythis site has a dual F&P stator using 2x 36 pole stators and black rotor cap producing 1.1kW output peak (DC) into a grid tie inverter. Operating voltage range into inverter is 45-90V so he's getting more than 400W per stator. He says it hasn't maxed out yet.

I'm hopping to design a converter which will allow these F&P stators to connect to batteries as one day I'm move out of the city and choose to go off grid :)

Cheers

David
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
flc1
Senior Member
Senior Member


Joined: 20 November 2011
Location: New Zealand
Online Status: Offline
Posts: 221
Posted: 18 August 2016 at 1:26am | IP Logged Quote flc1

guess it just goes to show that some people ( including myself) don't know as much about f n p performance as we thought we did. good work Dave.

Edited by flc1 on 18 August 2016 at 1:27am
Back to Top View flc1's Profile Search for other posts by flc1
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 18 August 2016 at 2:45am | IP Logged Quote DaveP68

Hi Fred

Thanks the feedback.

I understand that you have gearing system on your F&P turbine? That will be why you are getting over 1.1kW output from it. Also I think you mentioned you used to have batteries on your F&P wind turbine and the output was not much over 400W.

Just goes to show that when these F&P turbines are set up correctly using an MPPT inverter you can break past that so called 400W limit!!

Personally I had the impression that this website was for DIY? That's why I'm trying to put the knowledge gained about these F&P stators to get the optimum output on here. More info to follow to fill the blanks in for the non believers...


Cheers

David
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
flc1
Senior Member
Senior Member


Joined: 20 November 2011
Location: New Zealand
Online Status: Offline
Posts: 221
Posted: 18 August 2016 at 3:03am | IP Logged Quote flc1

thanks Dave, yea this is a free diy energy info shareing site for all to use,, not a free advertiseing, push your own product for profit site.

Edited by flc1 on 18 August 2016 at 3:06am
Back to Top View flc1's Profile Search for other posts by flc1
 
DaveP68
Senior Member
Senior Member
Avatar

Joined: 25 November 2014
Location: New Zealand
Online Status: Offline
Posts: 210
Posted: 25 May 2017 at 10:55am | IP Logged Quote DaveP68

fillm wrote:
Hi Dave,
I can not really see the point of giving output data into loads that do not represent anything that is useful like energy storage / battery charging or a grid tie and then secondly to get to the higher output the RPM is in a range where a wind turbine rarely operates at unless its in Antarctica. You might have some kind of controller I have not heard of to turn that data into something.
The voltage range of 16 to 137.5V is such a wide range and you have not given a purpose other than 86Ohm is the best load. Testing and posting data is great but what is normally an 86 ohm load and has a purpose. Also setting up Star delta switching ect to maintain maximum output at RPMs that can only be achieved in 40+ KLM wind is messy and doomed.
Dont get me wrong , I think the F&P is a great thing and is one of the few PMAs can be smashed by 100klm winds all day and not burn out and if it strong enough to take the battering.
We did a lot of testing a few years back and I cut my turbine teeth on the F&P and to date have not seen or come across a black rotor. But if the windings are not .8 or 1mm then I would think the output would be limited in real world testing and if it gets over 400W I would be surprised



I would like some form of response from you Phill conceding that the F&P 36 pole copper stators with black rotor caps out performs any 42 pole stator.

All the topics I've posted over the past 6 months prove it anyway.

You have gone completely silent, which can only mean one thing...
Back to Top View DaveP68's Profile Search for other posts by DaveP68
 
kitestrings
Regular Member
Regular Member


Joined: 23 April 2014
Location: United States
Online Status: Offline
Posts: 85
Posted: 26 May 2017 at 4:37pm | IP Logged Quote kitestrings

Personally I don't see this as a productive turn in the discussions. I've enjoyed following your work with different alternators, configurations and cap customization. Your work is impressive, well organized and well documented. Here's the but...but, it is in a controlled lab, if you will, and not exactly comparing apples to apples when put beside fillm's work IMO. The optimum output of an alternator is only one piece in a seemingly simple wind turbine.

I hope you continue. And, I hope that you, or someone can take what you've learned and apply it to the real-world application in the air. Even then I hope it is a discussion with mutual respect.

~ks
Back to Top View kitestrings's Profile Search for other posts by kitestrings
 


Page of 3 Next >>
In the news...
 
Post ReplyPost New Topic
Printable version Printable version
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot delete your posts in this forum
You cannot edit your posts in this forum
You cannot create polls in this forum
You can vote in polls in this forum

Powered by Web Wiz Forums version 7.8
Copyright ©2001-2004 Web Wiz Guide

This page was generated in 0.1250 seconds.
Privacy Policy     Process times : 0.03, 0, 0, 0.09