Author |
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 15 June 2017 at 2:24pm | IP Logged
|
|
|
I thought folks might be interested to see our latest turbine addition. I added a linear actuator (well hidden behind all the weatherization efforts) which operates off the CC to furl the tail. This is not for normal running mode operation, but is set up to (softly) shutdown the system when the input voltage to the controller goes over a preset voltage, currently about 125V. So if a windy overcast day turns sunny, and we no longer need the power.

It has a built-in potentiometer so the presets can be set, and triggered with one contact closure using one of the auxiliary relays.
 So far working pretty well. We'll see if it holds up thru all the different weather expectations.
~ks
|
Back to Top |
|
|
jorn Newbie

Joined: 30 December 2012 Location: Netherlands
Online Status: Offline Posts: 12
|
Posted: 16 June 2017 at 3:11pm | IP Logged
|
|
|
Kitestrings,
Next step is pitchcontrol? http://www.fieldlines.com/index.php/topic,145925.594.html
Rgds. Jorn
|
Back to Top |
|
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 16 June 2017 at 5:49pm | IP Logged
|
|
|
jorn,
No, I don't think so. That's a thread that has goes back ~2011 or '12 IIRC. They've done some creative stuff; midwoud1 & mbouwer, and I've enjoyed watching their progress.
To me, I like the simplicity of a furling tail design. I've run with this design now for over 30-yrs. I like that I have basically three moving parts up in the air, and all of the electronics and most of complexity are not 85' in the air.
My furling actuator can, and may fail - it is really just pulling a rope - but the turbine will still furl, all on its own. ~ks
|
Back to Top |
|
|
Warpspeed Guru

Joined: 09 August 2007 Location: Australia
Online Status: Offline Posts: 1533
|
Posted: 16 June 2017 at 11:07pm | IP Logged
|
|
|
Is that an electric automotive power steering rack ?
__________________ Cheers, Tony.
|
Back to Top |
|
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 17 June 2017 at 1:25pm | IP Logged
|
|
|
Wrspd,
No, it is a 12V (electro-mechanical) linear actuator. I took two rubber steering stabilizer boots and joined them with a piece of PVC to enclose the arm. The unique thing with this one is that it has a built in potentiometer, so you can set up to three preset positions. And, it has an auto-return feature which allows you to go to one position when the "ignition" wire is energized, and return to a second when the signal is removed. This is ideal in our case. It allows the furled, unfurled positions to be programmed and controlled with a single dry-contact operation.
~ks
|
Back to Top |
|
|
fillm Guru


Joined: 10 February 2007 Location: Australia
Online Status: Offline Posts: 723
|
Posted: 20 June 2017 at 10:10pm | IP Logged
|
|
|
As Always , nice work KS and the actuator with some easily settable stop points is handy if you just want a partial furl. I am a big advocate for manual furl and fit it standard to the OZ Wind Turbines. With me it is more born out of necessity with the power the GOE222 blades develop and back when I thought AXFX Alts were so to say " The Bees Knees"and I burnt up a few before adding it to the last one I built that now sits on a shelf marked with 'one day'a Var Pitch set.... when time permits.
I have had customers set up similar to what you have but more actuated / triggered on Wind speed and when using very large Dia GOE blade set. But I mostly recommend a simple correct sized weight hung on the cord or sliding down a star picket that does not allow the tail to return to the lower stop when the tail starts furling, it may take a few gusts to get it to the point where it goes over center. With a pin in the picket holes to stop it where required, this then gives a bit of movement on the tail to dampen any the side gusts.
Being able to safely park a turbine in any wind is paramount in my books and manual furl has been around 200years on pumpers so its a tried and proven method.
__________________ PhillM ...Oz Wind Engineering..Wind Turbine Kits 500W - 5000W ~ F&P Dual Kits ~ GOE222Blades- Voltage Control Parts ------- Tower kits
|
Back to Top |
|
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 21 June 2017 at 4:01pm | IP Logged
|
|
|
Thanks fillm. I'm pretty partial to off-set furling, and manual furling also. It just seems to be the most passive way to stop a turbine for any reason. Some folks on OP have demonstrated a similar results with variable-pitch rotor, but it is not without complexity, and with it, the potential for failure.
We actually dabbled with the idea of a ratchet on the yaw hinge that could be engaged from the ground. I had a handful of early sketches:

In the end I like the approach we have. I had been closing it down with a small hand winch. This just allows me to do it from the house, or PC. For a total shutdown, I furl the turbine and then connect the load bank. This brings it to a minimal rotational speed - less than 20 rpm I'd guess.
With the controller it gives us the option of having it close up based on input voltage. You can set a Vhi voltage, delay (how long there before it operates), and a Vlow, or reset (also with a delay). Still, I kept the hand winch there just to be safe.
Look forward to seeing more of your work. I hear great things about those GOE222 profile blades.
~ks
|
Back to Top |
|
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 22 June 2017 at 12:42pm | IP Logged
|
|
|
So last night was a pretty good test. Pretty high winds. I'd been in and out of the house watching things. I decided to try intentionally lower the trigger point to simulate a shut-down. I dropped the set-point to just above the input voltage I'd been seeing; ~95V IIRC.
True to from it tripped the actuator, furled the machine, and I watched the output drop from about 1,500-1,800 watts to maybe 200 watts within a half-minute or so. I then dropped in the load bank and the rotor dropped from 60-65 to about 20 rpm.
Hopefully it works when it is -10 F and snowing this winter. That will be the real test.
~ks
|
Back to Top |
|
|
flc1 Senior Member

Joined: 20 November 2011 Location: New Zealand
Online Status: Offline Posts: 229
|
Posted: 25 June 2017 at 12:57am | IP Logged
|
|
|
Gday Kitestrings,That looks to be a good system you have there. I will also be useing a 12volt dc , voltage activated actuator for my system,but setup a diffrent way, looking at your system has given me the idea to put the actuator up on the turbine itself,and run a couple of small feed cable up the centre of the pole or bleed off some power up there to operate it,,it could also furl itself in high winds without the actuator,,,,the actuator would simply push against a set point on the tail to furl it,with out being conected to the tail. The actuator I have is only about 120mm long with a thrust force of 900n (90kg) and a lock force of 2300n,and draws about 4 amps under max load, a slightly larger actuator than mine,with say 300mm stroke and same thrust power should do it. Can easily enclose the actuator from the weather. bugger!! I wish I had seen this post before I had started my rebuild . I guess I could still change things on my turbine as its still in the shed at the moment.
Edited by flc1 on 25 June 2017 at 2:24am
|
Back to Top |
|
|
DaveP68 Senior Member


Joined: 25 November 2014 Location: New Zealand
Online Status: Online Posts: 237
|
Posted: 25 June 2017 at 11:00am | IP Logged
|
|
|
Hi kitestrings
Nice work with your automated furling actuator system. Looks like you have more than "partial furling" control demonstrated with the last test. Better than any manual system.
That's a big drop from a peak of 1800 W down to 200 W and with the load bank added in down to 20 RPM.
From what I know about blade TSR, the RPM even in high winds will not be able to get above 50-60 RPM. The reason for the low, but "controlled" RPM is the blades are fully stalled. This keeps everything well within safe operating limits too.
You've forced the blades into a 'power coefficient' of less than 10 % of their optimum operating range which would normally extract the maximum amount of power.
Here's a 'tip speed ratio vs power coefficient' graph to illustrate what I mean, more for those that read this that may not understand what I'm referring too.

By the way have you seen my topic on Electronic Dynamic Braking?
Edited by DaveP68 on 25 June 2017 at 12:11pm
|
Back to Top |
|
|
kitestrings Regular Member

Joined: 23 April 2014 Location: United States
Online Status: Offline Posts: 89
|
Posted: 26 June 2017 at 12:59pm | IP Logged
|
|
|
I suspect it would be an interesting engineering study to model the effect on the airfoil as a turbine furls. Furling seems really simple and yet is probably one of the least (well) understood topics. This site has IMO one of the better illustrations that I’ve seen: http://www.thebackshed.com/windmill/Docs/Furling.asp
Still, the insert pictures might be a bit confusing to someone who’s never seen this (or that you’re trying to explain it too). Notice how all three show a perfectly round rotor path. So this is actually viewed from changing vantage point; one where you stay perpendicular to the plane of the blades.
In practice, there is an initial period, when the winds are light, where the tail does not leave its resting position against the lower stop. Gravity keeps it there, and there is simply a playful “teetor-tooter” balance between the thrust on the rotor and tail’s natural tendency to stay parallel to the wind stream. Most builders have the tail open a little (5-15 degrees) past the 90-degree mark so that at, or near, cut-in the turbine is at a starting position that is perpendicular to the wind.
As the wind increases of course the tail comes off this lower stop. The plane of the blades now transitions from a circle as “seen” by the wind to an ellipse. As the wind gets higher still, the area of the rotor becomes an ever decreasing ellipse; to the point where the plane of the blades and the tail are effectively in the same path. Where the blades stall along this progression might be challenging to calculate given the variables at work, but as DaveP suggests, I assume it happens if we have a workable design.
Even when you watch this is real time – it’s fascinating IMO – what you see, and what it appears that you see are at times at odds. It often looks as though the tail is the only thing that is wagging about. I liken it to watching a stage coach wheel that appears on film to be turning backwards ;>].
|
Back to Top |
|
|
DaveP68 Senior Member


Joined: 25 November 2014 Location: New Zealand
Online Status: Online Posts: 237
|
Posted: 06 July 2017 at 11:09am | IP Logged
|
|
|
Hi Kitestrings
This is how I see what you were trying to explain about how the "front on swept area" of the blades actually looks during furling as explained above.
No furling full swept area of blades.

Now 50 % furling with blades at 45 deg to the flow of the air stream.
 Now 75 % furling with blades at 67.5 deg to the flow of the air stream.
 This along with an offset angle of attack of blades to the wind flow is the reason for the big drop in power in the shaft feeding the PMA.
A much easier way to keep things under control like you have outlined above.
Well done and thanks again for your valued contribution to adding to the knowledge on this website.
Edited by DaveP68 on 06 July 2017 at 11:11am
|
Back to Top |
|
|