Posted: 08:31am 14 May 2023 Copy link to clipboard
Murphy's friend Guru
Well, maybe. All thermostats are not created equal. If the contacts are slow to open or/and the opening distance is insufficient, it will create a DC arc when the contacts *open*.
Once the arc is established, 'off' time no longer plays any role as long as there is solar power and a load to feed it.
Posted: 11:29am 14 May 2023 Copy link to clipboard
Confused Newbie
Hello Davo99, Yes, It was the Arduino board and the caps that I was referring to. I just wanted to get as close to what you used and any other unit you used.
JS.
Posted: 12:39pm 14 May 2023 Copy link to clipboard
phil99 Guru
I worded that poorly. I should have said the 'on' and 'off' times of the MOSFET. The MOSFET 'on' time needs to be short so that if the thermostat opens while it is on you want the MOSFET to switch off before the arc damages the contacts. The MOSFET 'off' time needs to be long enough to ensure the arc has extinguished and prevent the arc re-striking.
Having the thermostat switch the gate or gate power supply is the safer option.
Posted: 03:15pm 14 May 2023 Copy link to clipboard
Murphy's friend Guru
Understood, that is exactly what my system does.
Posted: 09:49pm 14 May 2023 Copy link to clipboard
Confused Newbie
Davo99, With what the lads are saying and what you say in your long post. In there any modifications you'd make. Any chance of a simple diagram. J.S