Aaron, I did some rough testing on my ozz inverter a few weeks ago, this were the numbers I noted, testing was done with especially resistive loads: I had 4 meters at hand, 3 uni-T true RMS meters (current clamp type) and 1 extech true rms voltage meter.
The AC meter is a chinese front panel meter and is actually accurate.
Measurement 1: on my AC meter 328W with my clamp meter: 2.2A 237VAC --> 521.4VA 8.0A 52.1V --> 417W
With this power level there is a substantial part reactive power I guess, all switched power supplies with a bad power factor so it seems?
328/417W -->78%
Measurement 2: on my AC meter 1335W
with my clamp meter: 5.92A 238VAC --> 1409VA 28.3A 51.85VDC --> 1468W
1335/1468 => 90.9%
Measurement 3 on my AC meter 2340W on my clamp meter: 10A 239.5VAC --> 2395VA 48.6A 51.3VDC --> 2493.18W
2340/2493 => 93.8%
Measurement 4
On my AC meter 3765W with my clamp meter: 15.8A 238.8V AC --> 3773VA 82.2A 49.7V --> 4085W 3765/4085 =>92.2%
Measurement 5:
on my AC meter 6122W with my clamp meter 27.2A 224V AC --> 6160VA 142A 48.5V --> 6887W 6122/6887 => 89%
My inverter is completely powering my house, so it's a real life example. I have some difficulties how I best calculate the efficiency of the inverter because of the reactive power involved. But I did with the worsted scenario. But either way it looks like my inverter has the highest efficiency around the 2500W mark.
The dropping of the voltage with higher loads has to do with the long cable run between inverter and battery. To be improved. I don't think I can improve more, just maybe the filter inductor between H-bridge and transformer, it gets hot, it only has 30mm˛ wire I think |