Transformer So since getting the initial system working, I have been considering my options for a larger main transformer. I have lots of the original size transformer (about 600va), which I had scavenged (they had too much noise for the intended application), and I stripped off the copper off some of them with the intention of removing and rebuilding the laminations.
 That would be a huge amount of work, with a bit of uncertainty, since unwinding and rewinding the laminations could result in higher core losses. So fortunately I found a great deal on a pair of 1500va Hammond 1182T117's on a local buy/sell. These have 4 120v windings, which I connected in series parallel to form the 120/120 volt output. Hammond transformer vs 600va transformer

I added a couple of turns to the 120v primaries to give them the same ratio as the 120v secondaries and then added 7 more turns to improve the standby draw slightly. I then added the new primary using #4 welding wire. To get the wire to fit, I removed the insulation, and replaced it with a layer of heat shrink. I used a large neo magnet with a center hole, to pull a steel slug with attached string through the heat shrink. I then pulled the 55' of wire through the 3/8" shrink tubing. A bit of a hassle, but it allowed me to get everything on there.

The DCR of the 240v winding ended up being .165ohms and the 47v winding .0131ohms. I used a 5.1:1 turns ratio.
I built an complicated mount for the transformer, that would have air flow around as much of the transfomer as possible. I have not tested it yet, so we will see if it works or not.

Since our typical hourly draw is ~1kw with peak hourly at 2.5kw (not including A/C), I think this transformer will be large enough to support things. I can always modify the second transformer to support A/C if global warming continues at it's present rate. |