Dual battery setup for off grid solar


Author Message
Solar Mike
Guru

Joined: 08/02/2015
Location: New Zealand
Posts: 1255
Posted: 01:30am 22 Jun 2026      

  Godoh said  Hi Mike I have another query on your Lead Carbon and LifePo4 setup.

So will the charger voltages that my regulators are set for ( 28.8 volts) damage or undercharge the Lithium batteries.

thanks
Pete


Lifepo4 cells top bulk voltage is 3.6v, generally however its good practice to only go to 3.5v/cell or 28 volts, this voltage suits L.Carbon as at 20°C that is also its max bulk voltage. If your charger is accurate and never exceeds 3.6/cell, they will work ok, I limit our CV period following bulk to 2 hours in the combined bank; if it was a Lifepo4 only bank, I limit the CV period to however long it takes for the BMS to achieve cell balance, usually 20 minutes or less.

Mike