OA47

Guru

Joined: 11/04/2012
Location: Australia
Posts: 899
Posted: 12:11am 19 Mar 2020
Copy link to clipboard 
Print this post

I have had issues with a project that is getting radio errors when a large soft start electric pump is in operation. To overcome this I have decided to try and locate the radio unit on the antenna. I will be using a 10 meter length of 4 core shielded cable between the radio unit and the RS232-USB converter to supply the 3V3, GND, Tx & Rx.

My question is should I ground the shield of the cable at both ends or just one?

OA47
 
PeterB
Guru

Joined: 05/02/2015
Location: Australia
Posts: 639
Posted: 12:37am 19 Mar 2020
Copy link to clipboard 
Print this post

G'Day OA47

Just to make a real mess of your day I would use a 6 core cable.
+5V or so to be regulated to 3.3V up the top
GROUND
Balanced + Rx
Balanced - Rx
Balanced + Tx
Balanced - Tx

Ground the shield at the bottom......probably

The reason for only grounding one end is that if both ends are grounded, current will flow in the shield and hence radiate noise.............I think.

Some smart young bloke will now shoot me down

Peter
 
BrianP
Senior Member

Joined: 30/03/2017
Location: Australia
Posts: 292
Posted: 03:07am 19 Mar 2020
Copy link to clipboard 
Print this post

  PeterB said  G'Day OA47

Just to make a real mess of your day I would use a 6 core cable.
+5V or so to be regulated to 3.3V up the top
GROUND
Balanced + Rx
Balanced - Rx
Balanced + Tx
Balanced - Tx

Ground the shield at the bottom......probably

The reason for only grounding one end is that if both ends are grounded, current will flow in the shield and hence radiate noise.............I think.

Some smart young bloke will now shoot me down

Peter


+1

B
 
mikeb

Senior Member

Joined: 10/04/2016
Location: Australia
Posts: 173
Posted: 05:29am 19 Mar 2020
Copy link to clipboard 
Print this post

  PeterB said  G'Day OA47

Just to make a real mess of your day I would use a 6 core cable.
+5V or so to be regulated to 3.3V up the top
GROUND
Balanced + Rx
Balanced - Rx
Balanced + Tx
Balanced - Tx

Ground the shield at the bottom......probably

The reason for only grounding one end is that if both ends are grounded, current will flow in the shield and hence radiate noise.............I think.

Some smart young bloke will now shoot me down

Peter


Not shoot you down but just clarify what is happening.
It's easier to picture if you draw the circuit out once you ground both ends.
You actually produce a 'shorted' turn. When you consider transformer action, and how magnetic fields propagate around a conductor, you can see that induced currents are imposed on your conductors within the shielded cable.
High frequency noise can be rectified, by the protection diodes built into most uC inputs, and produce a standing DC offset to the A/D converter also.
In my line of work I come across many Soft Starters, and Variable speed Drives, which cause havoc with signals.
A common solution to most of my problems is to pass my signal cables through a ferrite ring. No 'hard and fast' rules on number turns. Just as many as will fit.

Regards, Mike B.
Edited 2020-03-19 15:29 by mikeb
There are 10 kinds of people in the world.
Those that understand binary and those that don't.
 
Paul_L
Guru

Joined: 03/03/2016
Location: United States
Posts: 769
Posted: 06:36am 19 Mar 2020
Copy link to clipboard 
Print this post

Yep! Grounding both ends of the shield might produce a circulating loop current which can develop a voltage drop along either the ground wire or the shield. This would offset the ground reference voltage for the balance point of the Tx and Rx twisted pairs on one end or the other which would likely be amplified by one of the active elements and produce a background noise added to the signal. The Tx and Rx pairs should be true balanced differential pairs, tightly twisted so that any electrostaticaly induced voltage will be identical on both wires and thus cancel out at the receive end.

Paul in NY
 
Volhout
Guru

Joined: 05/03/2018
Location: Netherlands
Posts: 3496
Posted: 07:47am 19 Mar 2020
Copy link to clipboard 
Print this post

Grounding the shield:

It is very simple.

1/ disconnect the shielding of the serial cable, but leave all other wiring connected.
2/ Take a multimeter and measure ohms between the 2 devices (at the shield connections).
3/ Is it 0 ohm (or < 10 ohm) then there is another ground connection => option A.
  If > 10 ohm => option B

Option A:
Connect the shield only on one side (avoid ground loops), generally this is the controller side (computer). If it is a very dirty environment (i.e. strong RF signals) connect the other side through a capacitor (i.e. 10nF Y cap).

Option B:
Connect both sides of the shield. The shield will also act as a discharge wire to avoid  devices become charged.

Do this for every device in a RS485 or similar system. It is very common to see the shield only hard connected at the main computer/PLC, and capacitor coupled to every device.

Good luck,

Volhout

P.S. a Y capacitor is typically used becuase of it's design. When the capacitor fails it becomes and OPEN, not ashort.
Edited 2020-03-19 17:49 by Volhout
PicomiteVGA PETSCII ROBOTS
 
Tinine
Guru

Joined: 30/03/2016
Location: United Kingdom
Posts: 1646
Posted: 09:54am 19 Mar 2020
Copy link to clipboard 
Print this post

Yeah I would go straight for the 232—422 converter with termination resistors.
 
Turbo46

Guru

Joined: 24/12/2017
Location: Australia
Posts: 1590
Posted: 09:39pm 19 Mar 2020
Copy link to clipboard 
Print this post

RS485 is made for this situation. I would use an RS232/RS485 converter at each end with a 120 ohm termination resistor. Send 5 volts up the wire with a 3.3v regulator at the top. Earth the shield ONLY at the computer end to avoid earth currents inducing noise into the signal lines.

Communications should use a CRC with Acknowledge so the message can be repeated if corrupted.

Bill
Keep safe. Live long and prosper.
 
Tinine
Guru

Joined: 30/03/2016
Location: United Kingdom
Posts: 1646
Posted: 09:42am 20 Mar 2020
Copy link to clipboard 
Print this post

Pretty useful ebook:



RS422-RS485-Application-Guide-eBook.pdf
 
PeterB
Guru

Joined: 05/02/2015
Location: Australia
Posts: 639
Posted: 11:41pm 20 Mar 2020
Copy link to clipboard 
Print this post

Good morning All

Since non of you younger blokes want to pick a fight with me I will pick (another) fight with Paul.
Paul stated "tightly twisted cable"
Somewhere in the back of my mind there is something about "not too tight" and looking at photos in the eBook that seems about right. Is it that a tightly twisted cable will have increased C & L and hence reduced bandwidth ?
I await your responses.

Peter
 
Tinine
Guru

Joined: 30/03/2016
Location: United Kingdom
Posts: 1646
Posted: 02:11pm 21 Mar 2020
Copy link to clipboard 
Print this post

No, the way I remember it is a twist every 50mm. IIRC, this is from Serial Port Complete by Jan Axelson but I don't have the book to hand.

It appears that twisted pairs are more common than shields when it comes to differential transceivers.

Also, 10m probably wouldn't require termination resistors as I suspect that your BAUD is relatively low. 120R can be power hungry which would be a concern for a battery powered device.
 
Paul_L
Guru

Joined: 03/03/2016
Location: United States
Posts: 769
Posted: 09:57pm 21 Mar 2020
Copy link to clipboard 
Print this post

Good afternoon All

/KERFUFFLE MODE ON

Hey Peter, the question is how much to twist rather than to twist or not.

My answer is that I do not really know how tight the twist should be. I do know that Amphenol specs their CAT5E cables at 1Gbps or 350 MHz, CAT6 at 10 Gps or 550 Mhz, and CAT6A at 10 Gps or 650 MHz. The twist distance decreases from CAT5 to CAT6 to CAT6A. <www.cablesondemand.com>.

Within a twisted pair capacative and inductive coupling between the conductors would increase in proportion to the both the gauge and the length of the individual conductors. The length of the conductor would increase as the rate of twisting increases. However, resistance would decrease in proportion to the gauge of the conductors which would reduce the time constant (R*C). This would seem to indicate that the higher CAT numbers would load a transmitter more with increasing length.

Between the conductors of a twisted pair and other cables external to the CATn cable jacket both the inductive and capacative coupling would decrease with both decreasing twist length and increasing conductor gauge due to the increasing thickness of the conductor insulation and the cable jacket. This would seem to indicate that the higher CAT numbers would pickup less common mode interference from external circuitry.

It sounds like a toss up. I'd buy the highest CAT number you can afford.

/KERFUFFLE MODE OFF

Tinine -- I just disected a CAT6 cable here and found a twist about every 12 mm.

Paul in NY
 
Tinine
Guru

Joined: 30/03/2016
Location: United Kingdom
Posts: 1646
Posted: 11:02pm 21 Mar 2020
Copy link to clipboard 
Print this post

Heck there is even a calculator for this stuff

 
PeterB
Guru

Joined: 05/02/2015
Location: Australia
Posts: 639
Posted: 12:59am 22 Mar 2020
Copy link to clipboard 
Print this post

Australian overhead telephone lines are/were twisted. About 1 twist every 5 poles.
How does that fit in with your high level maths?

Peter
 
Turbo46

Guru

Joined: 24/12/2017
Location: Australia
Posts: 1590
Posted: 05:50am 22 Mar 2020
Copy link to clipboard 
Print this post

PeterB, I can recall telephone lines in the country on poles with 4-6 cross-arms with unpteen wires on them but I don't recall them being 'twisted'.

Paul, Kerfuffle is a good word. All OA47 asked was about earthing the shield after all.

He already may have the cable that he intends to use and it may or may not have twisted pairs and that would not be a deal breaker although twisted pairs would be better. I don't believe that TTL RS232 will be viable over 10 meters whether twisted pair cable or not.

As I said RS485 is made for this situation and 10 metres is peanuts for it. It should be OK using an untwisted pair over that distance if necessary. Regarding the 120 ohm resistors, yes they consume power but ONLY while a device is transmitting, I would still use them to reduce the effects of noise.

Bill
Keep safe. Live long and prosper.
 
PeterB
Guru

Joined: 05/02/2015
Location: Australia
Posts: 639
Posted: 06:10am 22 Mar 2020
Copy link to clipboard 
Print this post

G'Day Bill

If you looked closely at telegraph poles you would see 4 insulators every so often instead of the normal 2. This provided a way of crossing the wires over or twisting them and it was done to prevent cross talk to adjacent pairs.  
On the subject of RS232. It should be banned!

Peter

p.s. The 4 insulators also provided a better place to  build a nest I think.

P
Edited 2020-03-22 16:19 by PeterB
 
Tinine
Guru

Joined: 30/03/2016
Location: United Kingdom
Posts: 1646
Posted: 01:46pm 22 Mar 2020
Copy link to clipboard 
Print this post

As mentioned in another thread, my latest machine controller is based on the E100 which is the master of the RS-485/422 (full duplex) motion control network.
This is quite the noisy environment due to the high power servo drives driving brushless motors @20KHz PWM.

The network is constantly running @230K BAUD, every message has a checksum.
Never had a glitch and I'm only using unshielded phone cable.

This machine has never required the "Microsoft Reset" but the megabucks Trumpf laser, sitting next to my machine, constantly freezes, requiring a power-cycle. The laser machine has an industrial Windows PC (Siemens) on the front-end, talking to a Sinumerik CNC controller... MM/E100 ROCKS!  
 
lizby
Guru

Joined: 17/05/2016
Location: United States
Posts: 3009
Posted: 11:40pm 22 Mar 2020
Copy link to clipboard 
Print this post

  Turbo46 said  ... I don't believe that TTL RS232 will be viable over 10 meters whether twisted pair cable or not.


I've successfully run 3.3V TTL RS232 over 50 feet of Cat6 on several occasions. I'll admit that this has not been extensively tested, or tested at all in complicated environments.
PicoMite, Armmite F4, SensorKits, MMBasic Hardware, Games, etc. on fruitoftheshed
 
PeterB
Guru

Joined: 05/02/2015
Location: Australia
Posts: 639
Posted: 12:14am 23 Mar 2020
Copy link to clipboard 
Print this post

I still think RS232 should be banned

Peter
 
Paul_L
Guru

Joined: 03/03/2016
Location: United States
Posts: 769
Posted: 12:11pm 23 Mar 2020
Copy link to clipboard 
Print this post

RS232 works find over short distances in interference free areas, like where Lizby is in his barn. If you have interference or noise or are running more than 10 meters you should use a balanced method to screen out common mode junk pickup. Shielding only helps with capacitive coupled noise, it doesn't attenuate inductive coupled noise much at all.

Paul in NY.
 