Just not quite getting my rusty brain around temperature differential logic.
This simple code works, but doesn't allow for any differential. Like say 0.3°


If TmpCur<TmpTar Then 'Compare Current & Target temperature.
PumpStat="Running" 'Turn the Pump on.
pin(PinLed1)=1
else
PumpStat="Standby" 'Turn the Pump off.
pin(PinLed1)=0
endif


Main reason I want differential, is not for Solar control, but for when I'm using the Heat Pump. I want to reduce the amount of times it cycles on & off.

Cheers.
 
atmega8

Guru

Joined: 19/11/2013
Location: Germany
Posts: 724
Posted: 02:05pm 09 Apr 2016
Copy link to clipboard 
Print this post

.....???

HYSTERESIS ?
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 02:08pm 09 Apr 2016
Copy link to clipboard 
Print this post

That's the term I should have used.

Ie,

When temperature gets to 34°C, stop heating, but don't start again before it falls below say 33.6°.

Guessing it will need some sort of cycle flag.

Cheers
 
atmega8

Guru

Joined: 19/11/2013
Location: Germany
Posts: 724
Posted: 02:38pm 09 Apr 2016
Copy link to clipboard 
Print this post

This Is very simple.
HYSTERESIS is done by a Schmitt-Trigger.
You need a software Schmitt-Trigger like this:

if( Input > top)
LED = 1

else if( Input < min)
LED = 0Edited by atmega8 2016-04-11
 
robert.rozee
Guru

Joined: 31/12/2012
Location: New Zealand
Posts: 2428
Posted: 05:22pm 09 Apr 2016
Copy link to clipboard 
Print this post

try the following:


hyst = 1

If TmpCur<(TmpTar-hyst) Then 'Compare Current & Target temperature.
PumpStat="Running" 'Turn the Pump on.
pin(PinLed1)=1
endif

If TmpCur>(TmpTar+hyst) Then 'Compare Current & Target temperature.
PumpStat="Standby" 'Turn the Pump off.
pin(PinLed1)=0
endif


when the current temperature falls 1 degree below the target temperature, the pump is turned on.

when the current temperature rises 1 degree above the target temperature, the pump turns off.


cheers,
rob :-)
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 08:39pm 09 Apr 2016
Copy link to clipboard 
Print this post

  robert.rozee said   try the following:


hyst = 1

If TmpCur<(TmpTar-hyst) Then 'Compare Current & Target temperature.
PumpStat="Running" 'Turn the Pump on.
pin(PinLed1)=1
endif

If TmpCur>(TmpTar+hyst) Then 'Compare Current & Target temperature.
PumpStat="Standby" 'Turn the Pump off.
pin(PinLed1)=0
endif


when the current temperature falls 1 degree below the target temperature, the pump is turned on.

when the current temperature rises 1 degree above the target temperature, the pump turns off.


cheers,
rob :-)


Thanks Rob,

That's basically what I came up with once I rested my brain & could thing logically again.


If TmpCur<(TmpTar - TmpDif) Then
PumpStat="Running" 'Turn the Pump on.
pin(PinLed1)=1
else if TmpCur>(TmpTar) then
PumpStat="Standby" 'Turn the Pump off.
pin(PinLed1)=0
endif



Just not swinging on the high side of the set temp.

Will just have to add a minimum wait timer on it for when it's in heat pump mode now so the compressor unit can depressurise.

Have found a good example some else has done of Ardurino over here.
Phil.
 