BarkyJ Senior Member Joined: 26/04/2018 Location: New ZealandPosts: 114
Posted: 12:28am 11 May 2018
Copy link to clipboard
Print this post
Hi All
Just doing some planning. What is typically done for power cable from the windmill to whatever interface you guys use, and do you normally run 3 phase AC down the pole and rectify it at the ground, or rectify it on the windmill and run DC down the pole?
I found a good youtube clip which has an attached excel sheet for doing calculations which is quite useful.
https://www.youtube.com/watch?v=uS7CyTxAA4o
Based on this, my estimation whether I run AC or DC down the pole, I am in the region of requiring AWG 8 cable, which isnt cheap stuff. My estimation so far is 15m one way, so 30m of cable (assuming DC 2 wire).
Curious what others are using and where you sourced the cable from.
Thanks
BarkyJ Senior Member Joined: 26/04/2018 Location: New ZealandPosts: 114
Posted: 01:40am 11 May 2018
Copy link to clipboard
Print this post
http://www.nzev.co.nz/10mm-flexible-cable/
This is what I am currently looking at.
Warpspeed Guru Joined: 09/08/2007 Location: AustraliaPosts: 4406
Posted: 12:42am 12 May 2018
Copy link to clipboard
Print this post
You do not say what your system voltage is, or the expected current.
Ten mm squared cable has a resistance of .00172 ohms per linear meter, so 30m of that cable will have a resistance of .0516 ohms (at 20 Celsius).
The "normal" current rating for 10mm cable is 50 amps. I squared R gives a power loss of 129 watts at 50 amps for 30m of cable. Voltage drop at 50 amps would be 2.58 volts.
I have no idea if those are significant figures for your intended application.Cheers, Tony.
BarkyJ Senior Member Joined: 26/04/2018 Location: New ZealandPosts: 114
Posted: 05:03am 12 May 2018
Copy link to clipboard
Print this post
Sorry the system voltage at this stage is 36V.
Warpspeed Guru Joined: 09/08/2007 Location: AustraliaPosts: 4406
Posted: 06:16am 12 May 2018
Copy link to clipboard
Print this post
So its going to have about 7% loss at 50 amps.Cheers, Tony.