sPuDd Senior Member Joined: 10/07/2007 Location: AustraliaPosts: 251
Posted: 12:39pm 10 Jul 2007
Copy link to clipboard
Print this post
First up thanks to RossW, as I now have 24x EnerSys 2T500/2 500Ahr cells.
I bought these from 63ute on eBay after seeing your posting on the ones you bought.
http://myworld.ebay.com.au/63ute if looking for great deals on batts.
Now, all I can find on the EnerSys site is the info on discharging the cells.
I cannot find any specific info on charging other than a float charge of 2.265Vpc @ 25degC.
I intend to use the Outback 48V inverters with this setup, what should I be setting the charge to?
What about equalisation? Bulk, absorb etc?
Are these more like a gel cell, where you just set them for 13.8V and leave? I know the AGM's
hate the sort of high voltages that a wet cell can absorb.
Help much appreciated.
PS: I have some experience with this stuff and I'm an old school electronic tech by trade.
It should work ...in theory
RossW Guru Joined: 25/02/2006 Location: AustraliaPosts: 495
Posted: 08:15pm 10 Jul 2007
Copy link to clipboard
Print this post
I have the manufacturers details here, if you like:
sPuDd Senior Member Joined: 10/07/2007 Location: AustraliaPosts: 251
Posted: 11:24am 11 Jul 2007
Copy link to clipboard
Print this post
Thanks RossW,
if I read it right, fast charging for a 500Ah cell
would be 0.1 to 0.125 times capacity:
0.1 x 500 = 50amps
0.125 x 500 = 62.5amps
This would be done at 2.40Vpc for 10-15hrs max,
and only once a month.
I also figure that it would require about 0.08 to 0.1
times capacity for normal charging. 40-50amps.
That should suffice. I'm planning on about 2kW of
solar for now, and a few large wind gens in final
location. With Outback hardware in control this
strict regime should be easy enough.
sPuDd.. It should work ...in theory
AMUN-RA Senior Member Joined: 10/03/2007 Location: AustraliaPosts: 144
Posted: 09:14pm 11 Jul 2007
Copy link to clipboard
Print this post
sPuDd have you already got all your outback gear if not can quote for you from townsville also sharp solar panels 0428626707 Mick.Every day the sun shines
& gravity sucks= free energy.
RossW Guru Joined: 25/02/2006 Location: AustraliaPosts: 495
Posted: 11:23pm 11 Jul 2007
Copy link to clipboard
Print this post
Mick, I've already sent Trev a query on Panels, so I'll give you the same option (I'd like to support the locals if I can)...
I had a couple of panels stolen early this week (NOT HAPPY!)
I'm looking for some panels for my 48V system, but a bit cash-strapped at the moment. Looking for "best bang for buck" and ideally something I can expand later. To this end, considering two 210W/24V panels. Would consider 12V panels if price was competetive enough.
Can contact me via the board, or ph 0409-578-660 tks.