Home
JAQForum Ver 20.06
Log In or Join  
Active Topics
Local Time 06:08 09 May 2024 Privacy Policy
Jump to

Notice. New forum software under development. It's going to miss a few functions and look a bit ugly for a while, but I'm working on it full time now as the old forum was too unstable. Couple days, all good. If you notice any issues, please contact me.

Forum Index : Electronics : Charging info for EnerSys 2T500/2 cells

Author Message
sPuDd

Senior Member

Joined: 10/07/2007
Location: Australia
Posts: 251
Posted: 12:39pm 10 Jul 2007
Copy link to clipboard 
Print this post

First up thanks to RossW, as I now have 24x EnerSys 2T500/2 500Ahr cells.
I bought these from 63ute on eBay after seeing your posting on the ones you bought.
http://myworld.ebay.com.au/63ute if looking for great deals on batts.

Now, all I can find on the EnerSys site is the info on discharging the cells.
I cannot find any specific info on charging other than a float charge of 2.265Vpc @ 25degC.
I intend to use the Outback 48V inverters with this setup, what should I be setting the charge to?
What about equalisation? Bulk, absorb etc?
Are these more like a gel cell, where you just set them for 13.8V and leave? I know the AGM's
hate the sort of high voltages that a wet cell can absorb.

Help much appreciated.

PS: I have some experience with this stuff and I'm an old school electronic tech by trade.

It should work ...in theory
 
RossW
Guru

Joined: 25/02/2006
Location: Australia
Posts: 495
Posted: 08:15pm 10 Jul 2007
Copy link to clipboard 
Print this post

I have the manufacturers details here, if you like:

http://house.albury.net/07sep2006/TSafe-manual.pdf
http://house.albury.net/07sep2006/TSafe-summary.pdf

Cheers,
 
sPuDd

Senior Member

Joined: 10/07/2007
Location: Australia
Posts: 251
Posted: 11:24am 11 Jul 2007
Copy link to clipboard 
Print this post

Thanks RossW,

if I read it right, fast charging for a 500Ah cell
would be 0.1 to 0.125 times capacity:
0.1 x 500 = 50amps
0.125 x 500 = 62.5amps

This would be done at 2.40Vpc for 10-15hrs max,
and only once a month.

I also figure that it would require about 0.08 to 0.1
times capacity for normal charging. 40-50amps.

That should suffice. I'm planning on about 2kW of
solar for now, and a few large wind gens in final
location. With Outback hardware in control this
strict regime should be easy enough.

sPuDd..
It should work ...in theory
 
AMUN-RA

Senior Member

Joined: 10/03/2007
Location: Australia
Posts: 144
Posted: 09:14pm 11 Jul 2007
Copy link to clipboard 
Print this post

sPuDd have you already got all your outback gear if not can quote for you from townsville also sharp solar panels 0428626707 Mick.
Every day the sun shines
& gravity sucks= free energy.
 
RossW
Guru

Joined: 25/02/2006
Location: Australia
Posts: 495
Posted: 11:23pm 11 Jul 2007
Copy link to clipboard 
Print this post

  AMUN-RA said   sPuDd have you already got all your outback gear if not can quote for you from townsville also sharp solar panels 0428626707 Mick.


Mick, I've already sent Trev a query on Panels, so I'll give you the same option (I'd like to support the locals if I can)...

I had a couple of panels stolen early this week (NOT HAPPY!)

I'm looking for some panels for my 48V system, but a bit cash-strapped at the moment. Looking for "best bang for buck" and ideally something I can expand later. To this end, considering two 210W/24V panels. Would consider 12V panels if price was competetive enough.

Can contact me via the board, or ph 0409-578-660 tks.
 
Print this page


To reply to this topic, you need to log in.

© JAQ Software 2024