When choosing the inverter size, another trap to be wary of is the definition of "peak power output". I have an inverter rated at 600W continuous and 1000W peak, but it struggles to start a refrigerator that draws 0.3A at 240V = 72VA. After setting up a test rig I found the inverter can only sustain 1000W for about 1 cycle = 20mS. The motor start surge lasts around 400mS.
 
TassyJim

Guru

Joined: 07/08/2011
Location: Australia
Posts: 6283
Posted: 01:57am 20 Aug 2021
Copy link to clipboard 
Print this post

Some of the tables only look at Electrical power.
With a 1/2 HP motor the 1/2 HP may refer to mechanical power out.
There is a big difference.



This table is from my Franklin Electric bore pump manual. (3 wire includes earth)
I have used the 60Hz table to make our USA friends feel the love.

Taking the 1/2 HP (0.37kW) as an example.
Power in = Volts X amps X power factor
Power out = Power in X efficiency
The table lists nominal power as 0.37kW and Pmax at 0.60kW
For 115V, the current is 12 amps with starting current of 46 amps (That would be worst case)

At 100% load
Power in  = 115 x 12 x 0.72 = 993.6 W
Power out = 996.3 x 0.62    = 616 W ** matches the 0.6 kW Pmax in the table

At 50% load
Power in  = 115 x 12 x 0.51 = 703.8 W
Power out = 703.8 x 0.50    = 352 W

I have never bothered to measure the starting current on the pump. I miss the peak reading meters I had to play with 25 years ago.
I have CTs and CROs so maybe one day.
I might even make a micromite powered peak meter.

Jim
VK7JH
MMedit
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 7938
Posted: 06:46am 20 Aug 2021
Copy link to clipboard 
Print this post

Thanks Jim - excellent post!

Those are nice, low inrush pumps. I suspect they are skinny, with a long, thin armature (lower inertia). Also, the load on a bore pump, once the pipe is full, is quite gentle as it only lifts from the water surface height, not the bottom.

Up until my retirement I very rarely saw a motor with hp specification. They have been only been kW rated for many years now. The hp rating ones were usually reclaimed units for fans and pumps that were being re-used because they hadn't had much actual service use. We usually had the FLC to work with anyway, but we did occasionally get caught out with a pump that had to have an overload change at commissioning because the FLC didn't tie in with what we expected from the kW rating. Some of that was simply because the control panel was ordered before the pump and they turned up with a different rating!

Incidentally, the starting current of a motor is always the same at a given voltage. It doesn't matter if the motor normally runs light or at full load. The value of the starting current is a function of the magnetization current, iron losses and ratio of armature to stator windings and these are decided at the motor design stage. The length of the starting current surge is dependent on the inertia of the armature and load - and sometimes (particularly with fans) it can be quite long.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
Preliminary MMBasic docs & my PCB designs
 
lizby
Guru

Joined: 17/05/2016
Location: United States
Posts: 3378
Posted: 12:34pm 20 Aug 2021
Copy link to clipboard 
Print this post

  phil99 said  When choosing the inverter size, another trap to be wary of is the definition of "peak power output".

Right. If my inverter won't start the water pump (shallow well), I have a PICAXE cycle-slicing "slow start" circuit built which, at a minimum, will start a 1/3rd hp motor as tested.

Thanks, Jim. I suspect that's what I'm seeing with the FLC calculators--they are assuming an input of 373 watts, not a working output of 1/2hp which is the consideration for the nameplate FLC. And indeed, since they can't know the characteristics of the specific motor in question, how could they know what wattage input would produce 1/2 hp of work? The pump is not easily accessible to me, but I'll try to get to it to see if it has an FLC/FLA number on it.

I hope not to have to try the slow start circuit.
PicoMite, Armmite F4, SensorKits, MMBasic Hardware, Games, etc. on fruitoftheshed
 
lizby
Guru

Joined: 17/05/2016
Location: United States
Posts: 3378
Posted: 11:40am 21 Aug 2021
Copy link to clipboard 
Print this post

Here is my tracking chart with the water pump added. It's the blue line rising from -20 -- since I'm just looking at on/off, I arbitrarily set -20 as off and -5 as on. Similarly, the freezer off is -15 and on is 0.


The chart shows a curve, which isn't accurate. Each horizontal period of resolution is 6 minutes. The pump runs for about 1 minute. It might be better represented as a vertical line, but I don't know how to do that with this google chart.

The DR-Kit, LR-BR, and Up lines represent temperatures of the hot water feed pipes for my 3 heating zones. They're flatlined here because it's summer, and no heat is called for.

~
Edited 2021-08-21 22:11 by lizby
PicoMite, Armmite F4, SensorKits, MMBasic Hardware, Games, etc. on fruitoftheshed
 
lizby
Guru

Joined: 17/05/2016
Location: United States
Posts: 3378
Posted: 02:25pm 26 Aug 2021
Copy link to clipboard 
Print this post

I added another Tasmota-ized Sonoff PowR2 inline with my boiler. It's summer, so it rarely comes on, but here it is:



I didn't catch it on the Tasmota web page when it first came on, so didn't see the already averaged high load (not real peak), but it settled at 151 watts. It was on for 4 minutes and 9 seconds, and consumed (as reported by this device) 10 watt-hours. (That works out: 151 watts divided by 60 minutes per hour times 4 minutes equals 10 watt hours.)

This gives me confidence that when I hook it up with the AIMS auto-transfer inverter (separate from the one for the water pump), the 100Ah battery will give me heat for some significant period of time if the power goes out, though I'm going to need more batteries if I am not to exceed a C/20 usage.

~