  KeepIS said  Actually I think this might be DS1820 The dev markings are mostly worn off and it was the result of the Test app that made sense of what was left on the case Mike.
These screens are with the DS1820? device mentioned above, using 800 ms conversion time stops 1000 error. Result multiplied by 8 as noted by Jim in an earlier post, gives the correct temp to +- 1/2 a deg.
Mike
Posted: 05:14am 22 Jul 2020
see here for an explanation:
https://www.maximintegrated.com/en/design/technical-documents/app-notes/4/4377.html
the DS18S20 is designed to be a drop-in replacement for the DS1820 (note: no letter between the digits). as such, it performs a 12-bit conversion by default, taking 750ms. using just the function I=DS18B20(pin), the micromite attempts to do a 200ms conversion, which isn't supported. it looks like this may be why things fail.
Daniel, would you mind trying the following with your problematic sensor:
DO
 DS18B20 START pin, 3
 PAUSE 1000
 PRINT DS18B20(pin)*8
LOOP
i suspect you will then see sane values from the 'fake' sensor. the multiplication by 8 is due to the temperature being made available in a different format to that used by the DS18B20. getting extra bits of resolution out of the DS1820/DS18S20 requires a bit more trickery.
it could well be that the sensors we have been calling 'fake' are in fact just old-stock DS1820 or DS18S20 parts. it may also be that the arduino library the original poster has been using checks the type of the sensor and adjusts its timing and behaviour accordingly.
rob   :-)
Edited 2020-07-22 15:41 by robert.rozee
KeepIS
Posted: 05:58am 22 Jul 2020
Hi Rob, you may have my post mixed up with another, however as an FYI, delays make no difference to its use in the CMM2, and it still displays 1000 as expected with delays as this device is not the device that should be used in the CMM2, however it works ok with the resolution change.
I can get full data from it with the Test program used for testing fakes, and yes the jury is out on that fake report for this device, likely the program is not fully accounting for the variation in this old sensor.
Mike.
Posted: 06:05am 22 Jul 2020
i think you're right! have also just been looking through the arduino library Daniel was using, and it looks like it supports around half a dozen variation on the device. so there may be half a dozen different 'genuine' parts, with various 'clones'/'fakes' of each one. all entirely confusing!!!
rob   :-)
blade
Posted: 09:38am 22 Jul 2020
i would not be connecting the ground and vcc terminals together..u could still use the   internal power supply but  put an 1n4004 into your  main power line input i see you have the fet   there ..but  now add power to the vcc input  but draw it before the power comes into the 1n4004..u may need to regulate for 3.3 volt or 3.0 volt etc,, but  you should have the  regulator to give 3.0 volt or what ever it  requires,,probably  just a  zener and a resistor would do it i think for the reference voltage to the sensor....
reference  your first  schematic..i am looking at .it`s getting noisy power  supply i think....throwing it to give an either high  briefly.
EDIT:::sozz i  made a mistake with the input power to the sensor module there.
Edited 2020-07-22 20:13 by blade
Amnesie
Posted: 08:51pm 28 Jul 2020
Hi all,
to "close" this topic and give some final feedback after the 100% original DS18b20 sensors arrived:
As I said: no problem on my maximite. The original DS18b20 work just fine!
Although my fake sensors work with my arduino library on the atmega328p, I couldn't get them to work with the maximite. The only soloution was to buy original ones. Problem solved.
I am posting this in case anybody comes across the same problem in the future.
Some fake sensors will work on the maximite, some will not.
Greetings
Daniel
Posted: 07:38am 07 Aug 2020
Hi All,
I went and ordered some "DS18b20" devices and found the following
The 2 I bought from MOUSER.COM proved to be genuine.
I bought one from Jaycar Electronics which is mounted on a small PCB substrate and whilst both read a temperature and responded as expected when I held a soldering iron near them the Jaycar module comes up as a FAKE.
Stay away from these Jaycar Modules
Now when I run the tests, the fake returns a value in 232 ms whereas the genuine was 692ms (I think from memory)
However there was a temperature difference of approximately 2 degrees C (fake was lower) between the 2 just measured at ambient room temperature (fake read 24.5 the genuine 26.5).
I will run some tests with both bonded together so I should be able to see the variations at various temperatures.
But the difference is quite pronounced and I pose the argument that you should not use the fakes unless you have calibrated against a known source but even then how reliable are they?
Kind Regards
Posted: 08:07am 07 Aug 2020
Too late Mick,
I bought one early this week but haven't plugged it in yet.
Posted: 02:24am 08 Aug 2020
Now I have a 'suspect' chip to play with, I will refine the testing program.
Mick,
The first time I ran the program, time was 720mS
Then I used the inbuilt TEMPR function and then ran my program again.
This time the time was 180mS
So the Jaycar chip is responding to the command to set resolution.
> RUN
MM.ONEWIRE  1
Conversion time:  720.095
The temperature is: 18.812 degrees C
on DS18B20 (FAKE!!!) with ROM Code 28 AA 42 A3 41 14 01 D5 using External Power.
> print tempr(42)
18.75
> RUN
MM.ONEWIRE  1
Conversion time:  180.292
The temperature is: 18.750 degrees C
Can you run the program on the suspect chip again and tell me what ROM code you get?
Posted: 03:45am 08 Aug 2020
are you using an MX170/470 based micromite, or a CMM2? based upon the source code of the interpreter, the CMM2 seems to use quite different (although still in the ballpark) timing for one-wire communications.
rob   :-)
Posted: 04:59am 08 Aug 2020
I am using a CMM2. IT has no trouble reading my suspect module.
With the Jaycar modules, the "fake" claim comes from the serial number not complying with known ranges.
It is possible that Maxim have started using the high value serial numbers.
So far, I know that the one I have correctly changes between 10 and 12 bit resolution and the time taken for each resolution is correct.
The only chips we have had that can't be read with the CMM2/micromite code are the ones that started this thread. I would love to have one of them to play with but too far away...
The DS1820/DS18S20 chips are not catered for with the builtin TEMPR function but can be read with a basic subroutine OK.
I will convert the rest of the Arduino code into MMBasic and see what else I can find.
Posted: 05:14am 08 Aug 2020
Hi Jim, All,
Ok No worries, I am using a CMM2 as well directly on the 3 pads near the ARM chip
Here are my results
The Jaycar Module
MM.ONEWIRE  1
Conversion time:  176.335
The temperature is: 23.500 degrees C
on DS18B20 (FAKE!!!) with ROM Code 28 AA EE 63 3F 14 01 E5 using External Power.
The Mouser Part
MM.ONEWIRE  1
Conversion time:  610.162
The temperature is: 26.125 degrees C
on DS18B20 (Genuine) with ROM Code 28 98 4F 9B 09 00 00 73 using External Power.
EDIT ****  Note the different temperatures. they were stored in the same bag.. My CMM2 was on less than 30sec each time
Kind Regards
Edited 2020-08-08 15:17 by bigmik
Andrew_G
Posted: 06:15am 08 Aug 2020
Hmmm,
I have ten DS18B20s chips in use around the house all giving sensible results (ie +/- a degree). I also have several new ones.
I've tried Jim's program on two of the new ones - each on a MM170 and CMM2. All four trials say "FAKE" but give realistic temperatures.
I've also tried one of my long-cabled waterproof ones on the MM170 - "FAKE" but again with OK temperatures.
Cheers,
Andrew
Posted: 07:14am 08 Aug 2020
OK,
The "Fake" claim is based on the 6th and 7th bytes of the rom code. They are supposed to be zero. It is possible that that assumption is no longer valid.
Mick's device has the same values as mine. "14 01" so probable from the same source
Here is some code to try.
The first run should be after applying power to the DS18B20 to see what the reset values are.
The first 2 values of the scratchpad should be "50 05" immediately after power-up.
The program cycles through all valid resolutions and times them.
There are a few other checks that can be made but that's enough to start with.
 'DS18x20 test code by TassyJim
 DIM INTEGER PinNbr = 42
 PRINT
 PRINT
 PRINT "Family name: ";FamilyName$(PinNbr)
 PRINT "Rom Code:    ";getRomCode$(PinNbr)
 PRINT "ScratchPad:  ";getScratchpad$(PinNbr)
 IF powerMode(PinNbr) THEN
   PRINT "Power mode   External"
 ELSE
   PRINT "Power mode   Parasitic"
 ENDIF
 PRINT
 FOR n = 9 TO 12
 PRINT
   x = setResolution(PinNbr, n)
   TIMER = 0
   PRINT "Temperature: ";getTemp(PinNbr);" ";TIMER;"mS,";n;" bit"
 NEXT n
END
FUNCTION getRomCode$(PinNbr AS INTEGER)
 ' get ROM Code - useful if you want more than 1 device on wire
 LOCAL INTEGER a1,a2,a3,a4,a5,a6,a7,a8
 ONEWIRE WRITE PinNbr,1,1,&h33 'read ROM code
 ONEWIRE READ PinNbr,0,8,a1,a2,a3,a4,a5,a6,a7,a8
 getRomCode$ = HEX$(a1,2)+" "+HEX$(a2,2)+" "+HEX$(a3,2)+" "+HEX$(a4,2)+" "+HEX$(a5,2)+" "+HEX$(a6,2)+" "+HEX$(a7,2)+" "+HEX$(a8,2)
END FUNCTION
FUNCTION getScratchpad$(PinNbr AS INTEGER)
 'ONEWIRE Write PinNbr,1,9,&h55,a1,a2,a3,a4,a5,a6,a7,a8  'read from scratchpad
 ONEWIRE WRITE PinNbr,1,2,&hcc,&hbe
 ONEWIRE READ PinNbr,0,8,a,b,c,d,e,f,g,h
 getScratchpad$ = HEX$(a,2)+" "+HEX$(b,2)+" "+HEX$(c,2)+" "+HEX$(d,2)+" "+HEX$(e,2)+" "+HEX$(f,2)+" "+HEX$(g,2)+" "+HEX$(h,2)
END FUNCTION
FUNCTION powerMode(PinNbr AS INTEGER) AS INTEGER
 ' check whether power external (1) or parasitic (0)
 ONEWIRE RESET PinNbr
 ONEWIRE WRITE PinNbr, 1,2,&hcc, &hb4
 ONEWIRE READ PinNbr,4,1,powerMode
END FUNCTION
FUNCTION getFamily(PinNbr AS INTEGER) AS INTEGER
 getFamily = VAL("&h"+LEFT$(getRomCode$(PinNbr),2))
END FUNCTION
FUNCTION FamilyName$(PinNbr AS INTEGER)
 LOCAL INTEGER fn
 fn = getFamily(PinNbr)
 SELECT CASE fn
   CASE 16
     FamilyName$ = "DS1820/DS18S20"
   CASE 34
     FamilyName$ = "DS18S22"
   CASE 40
     FamilyName$ = "DS18B20"
   CASE ELSE
     FamilyName$ = "Unknown"
 END SELECT
END FUNCTION
FUNCTION setResolution(PinNbr AS INTEGER,r AS INTEGER)
 r = r-9
 IF r < 0 THEN r = 0
 IF r > 3 THEN r = 3
 r = r*32+31
 ONEWIRE WRITE PinNbr, 1,5,&hcc, &h4E, &hFF,&hFF,r
END FUNCTION
FUNCTION getTemp(PinNbr AS INTEGER) AS FLOAT
 LOCAL INTEGER fn, t, T1, T2, a,b,c,d,e,f,g,h
 LOCAL FLOAT Value
 power = powerMode(PinNbr)
 ONEWIRE RESET PinNbr                        ' reset before command
 ONEWIRE WRITE PinNbr, 8, 2, &hcc, &h44      ' start conversion
 'read external when b goes high, for parasitic just wait
 IF power = 0 THEN
   PAUSE 750
 ELSE
   t = TIMER
   DO
     IF TIMER - t > 1000 THEN
       Value = 1000
       EXIT DO
     ENDIF
     ONEWIRE READ PinNbr, 4 , 1 , b            ' conversion done?
   LOOP UNTIL b = 1
 ENDIF
 IF Value = 0 THEN ' we have not timed out yet
   ONEWIRE WRITE PinNbr, 1, 2, &hcc, &hbe      ' command read data
   ONEWIRE READ PinNbr, 2, 2, T1, T2           ' get the data
   SELECT CASE fn
     CASE 16 'DS18S20 or DS1820
       IF T2 AND &h80 THEN       'if MSB of T2=1 then negative
         'Read 12bit resolution and adjust
         'truncate 0.5deg value (or use integer division \)
         T1 = T1 AND &hFE
         T1=T1 / 2                   'make whole degrees
         'add compensation values read from scratchpad
         T1=T1*16                  'make lsb 1/16 degree
         T1 = T1 -4 +(16 - g)    'add 12 bit value
         'take 2s complement
         T1 = (T1 XOR &hFF) + 1
         Value = -T1/16                'make decimal value in degrees
       ELSE                              'positive temp
         Value = T1 / 2                '9bit value
         T1 = T1 AND &hFE      'truncate 0.5deg(or use integer division \)
         Value = T1/2- 0.25 + (16 - g) /16   '12 bit value
       ENDIF
     CASE 34, 40 ' DS18S22 or DS18B20
       IF T2 AND &b1000 THEN       'negative temp
         'make 2s complement (1s complement+1)
         T2 = (T2 XOR &hFF)
         T1 = (T1 XOR &hFF)+1
         IF T1=1 THEN T2=T2+1        'add the carry if required
         Value = -((T2 AND &b111) * 256 + T1) / 16
       ELSE                            'positive temp
         Value = ((T2 AND &b111) * 256 + T1) / 16
       ENDIF
     CASE ELSE
       Value = 1000
   END SELECT
 ENDIF
 getTemp= Value
END FUNCTION
Posted: 07:20am 08 Aug 2020
Hi Jim, All,
I have done my test with the 2 types bound together with a small cable tie.
The Mouser unit on pin(35) the Jaycar on pin(37)
Using this code
mik:
print "Mouser = "; tempr(35),"Jaycar = ";tempr(37)
pause 2000
goto mik:
I got these results after heating, carefully, with my heat gun from around 20cm away to roughly 60c and letting them gradually cool... each check is 2 seconds apart.
Mouser =  54.25 Jaycar =  54
Mouser =  53.75 Jaycar =  53.5
Mouser =  53.25 Jaycar =  52.75
Mouser =  52.75 Jaycar =  52.25
Mouser =  52.25 Jaycar =  51.75
Mouser =  51.75 Jaycar =  51.25
Mouser =  51.25 Jaycar =  50.75
Mouser =  50.75 Jaycar =  50.25
Mouser =  50.25 Jaycar =  49.75
Mouser =  49.75 Jaycar =  49.5
Mouser =  49.25 Jaycar =  49
Mouser =  48.75 Jaycar =  48.5
Mouser =  48.25 Jaycar =  48
Mouser =  47.75 Jaycar =  47.75
Mouser =  47.5  Jaycar =  47.25
Mouser =  47    Jaycar =  46.75
Mouser =  46.5  Jaycar =  46.5
Mouser =  46.25 Jaycar =  46
Mouser =  45.75 Jaycar =  45.5
Mouser =  45.25 Jaycar =  45
Mouser =  45    Jaycar =  44.75
Mouser =  44.5  Jaycar =  44.25
Mouser =  44.25 Jaycar =  44
Mouser =  43.75 Jaycar =  43.5
Mouser =  43.5  Jaycar =  43.25
Mouser =  43    Jaycar =  43
Mouser =  42.75 Jaycar =  42.5
Mouser =  42.5  Jaycar =  42.25
Mouser =  42    Jaycar =  42
Mouser =  41.75 Jaycar =  41.5
Mouser =  41.5  Jaycar =  41.25
Mouser =  41.25 Jaycar =  41
Mouser =  40.75 Jaycar =  40.75
Mouser =  40.5  Jaycar =  40.25
Mouser =  40.25 Jaycar =  40
Mouser =  40    Jaycar =  39.75
Mouser =  39.5  Jaycar =  39.5
Mouser =  39.25 Jaycar =  39.25
Mouser =  39    Jaycar =  39
Mouser =  38.75 Jaycar =  38.75
Mouser =  38.5  Jaycar =  38.5
Mouser =  38.25 Jaycar =  38
Mouser =  38    Jaycar =  37.75
Mouser =  37.75 Jaycar =  37.5
Mouser =  37.5  Jaycar =  37.25
Mouser =  37.25 Jaycar =  37
Mouser =  37    Jaycar =  36.75
Mouser =  36.75 Jaycar =  36.5
Mouser =  36.5  Jaycar =  36.5
Mouser =  36.25 Jaycar =  36.25
Mouser =  36    Jaycar =  36
Mouser =  35.75 Jaycar =  35.75
Mouser =  35.75 Jaycar =  35.5
Mouser =  35.5  Jaycar =  35.5
Mouser =  35.25 Jaycar =  35.25
Mouser =  35    Jaycar =  35
Mouser =  34.75 Jaycar =  34.75
Mouser =  34.5  Jaycar =  34.5
Mouser =  34.25 Jaycar =  34.25
Mouser =  34    Jaycar =  34.25
Mouser =  33.75 Jaycar =  33.75
Mouser =  33.5  Jaycar =  33.5
Mouser =  33.25 Jaycar =  33.25
Mouser =  33    Jaycar =  33
Mouser =  33    Jaycar =  32.75
Mouser =  32.75 Jaycar =  32.75
Mouser =  32.5  Jaycar =  32.5
Mouser =  32.5  Jaycar =  32.25
Mouser =  32.25 Jaycar =  32.25
Mouser =  32    Jaycar =  32
Mouser =  32    Jaycar =  31.75
Mouser =  31.75 Jaycar =  31.75
Mouser =  31.75 Jaycar =  31.5
Mouser =  31.5  Jaycar =  31.5
Mouser =  31.5  Jaycar =  31.25
Mouser =  31.25 Jaycar =  31.25
Mouser =  31    Jaycar =  31
Mouser =  31    Jaycar =  30.75
Mouser =  30.75 Jaycar =  30.75
Mouser =  30.75 Jaycar =  30.5
Mouser =  30.5  Jaycar =  30.5
Mouser =  30.5  Jaycar =  30.25
Mouser =  30.25 Jaycar =  30.25
Mouser =  30    Jaycar =  30
Mouser =  29.75 Jaycar =  29.75
Mouser =  29.5  Jaycar =  29.5
Mouser =  29.25 Jaycar =  29.25
Mouser =  29    Jaycar =  29
Mouser =  29    Jaycar =  28.75
Mouser =  28.75 Jaycar =  28.75
Mouser =  28.5  Jaycar =  28.5
Mouser =  28.5  Jaycar =  28.25
Mouser =  28.25 Jaycar =  28.25
Mouser =  28    Jaycar =  28
Mouser =  27.75 Jaycar =  27.75
Mouser =  27.75 Jaycar =  27.5
Mouser =  27.5  Jaycar =  27.5
Mouser =  27.5  Jaycar =  27.25
Mouser =  27.25 Jaycar =  27.25
Mouser =  27    Jaycar =  27
Mouser =  27    Jaycar =  26.75
Mouser =  26.75 Jaycar =  26.75
Mouser =  26.75 Jaycar =  26.5
Mouser =  26.5  Jaycar =  26.5
Mouser =  26.5  Jaycar =  26.25
Mouser =  26.25 Jaycar =  26.25
Mouser =  26    Jaycar =  26
Mouser =  25.75 Jaycar =  25.75
The cooling curve is almost exactly identical and all readings are within 0.25degrees
If the Jaycar unit is a fake it's a good fake.
This is how I tested them.
This is the markings for each, both appear to be laser etched.
Kind Regards
Posted: 07:27am 08 Aug 2020
Hi Jim, All,
This is the results of your test code
MOUSER
Family name: DS18B20
Rom Code:    28 98 4F 9B 09 00 00 73
ScratchPad:  64 01 00 00 3F FF 0C 10
Power mode   External
ScratchPad:  64 01 FF FF 1F FF 0C 10
Temperature:  22.5  93.301mS, 9 bit
ScratchPad:  68 01 FF FF 3F FF 08 10
Temperature:  22.5  169.566mS, 10 bit
ScratchPad:  68 01 FF FF 5F FF 08 10
Temperature:  22.375  322.199mS, 11 bit
ScratchPad:  66 01 FF FF 7F FF 0A 10
Temperature:  22.25  627.221mS, 12 bit
JAYCAR
Rom Code:    28 AA EE 63 3F 14 01 E5
ScratchPad:  64 01 00 00 3F FF 20 10
Power mode   External
ScratchPad:  64 01 FF FF 1F FF 1F 10
Temperature:  22.5  104.914mS, 9 bit
ScratchPad:  68 01 FF FF 3F FF 3F 10
Temperature:  22.5  192.78mS, 10 bit
ScratchPad:  68 01 FF FF 5F FF 5F 10
Temperature:  22.5  368.593mS, 11 bit
ScratchPad:  68 01 FF FF 7F FF 7F 10
Temperature:  22.4375  720.245mS, 12 bit
Kind Regards
Posted: 07:37am 08 Aug 2020
I tend to agree that the Jaycar ones are usable.
Comparing my two devices, the Jaycar is slower but does do all resolutions.
A genuine device:
Purchased from RS within the last 12 months
Rom Code:    28 A6 56 79 0B 00 00 03
ScratchPad:  50 05 4B 46 7F FF 0C 10
Power mode   External
ScratchPad:  50 05 FF FF 1F FF 0C 10
Temperature:  19.5  93.463mS, 9 bit
ScratchPad:  38 01 FF FF 3F FF 08 10
Temperature:  19.5  169.916mS, 10 bit
ScratchPad:  38 01 FF FF 5F FF 08 10
Temperature:  19.5  322.736mS, 11 bit
ScratchPad:  38 01 FF FF 7F FF 08 10
Temperature:  19.4375  628.411mS, 12 bit
A suspect device:
Purchased from a Jaycar reseller last week
Rom Code:    28 AA 42 A3 41 14 01 D5
Power mode   External
ScratchPad:  50 05 FF FF 1F FF 1F 10
Temperature:  20  107.037mS, 9 bit
ScratchPad:  40 01 FF FF 3F FF 3F 10
Temperature:  20  196.968mS, 10 bit
ScratchPad:  40 01 FF FF 5F FF 5F 10
Temperature:  20.125  376.948mS, 11 bit
ScratchPad:  42 01 FF FF 7F FF 7F 10
Temperature:  20.125  736.821mS, 12 bit
Andrew_G
Posted: 07:50am 08 Aug 2020
Jim,
I get this from my CMM2 using one of the "Fake" units
Rom Code:    28 07 00 07 AD 20 02 86
ScratchPad:  50 05 FF FF 7F FF 0C 10
Power mode   External
Temperature:  20  60.083mS, 9 bit
ScratchPad:  40 01 FF FF 3F FF 10 10
Temperature:  20  103.152mS, 10 bit
ScratchPad:  40 01 FF FF 5F FF 10 10
Temperature:  20.125  189.558mS, 11 bit
ScratchPad:  42 01 FF FF 7F FF 0E 10
Temperature:  20.125  362.206mS, 12 bit
Is this what you expect?
Andrew
Posted: 08:19am 08 Aug 2020
According to https://github.com/cpetrich/counterfeit_DS18B20
Your rom code is wrong due to the "20 02" last two numbers which should be zeros.
Based on the timing for 12 bit conversion, your device is group A2.
"significant number of sensors with offsets outside the ±0.5 C range at 0 °C"
Andrew_G
Posted: 12:37am 09 Aug 2020
Thanks Jim.
I read the Github article - very interesting.
Yes mine are clones/fakes/imitations in the A2 group (and there is nothing on the indent) but they could be worse.
Whilst I'd prefer genuine, and am happy to support the genuine supply chain, I can live with the 0.5C error margin (I calibrate them against an assumed good one and apply a correction (which I can update via HC-12) - at least they are all consistently wrong.
I'm not sure what the error at 0C means but fortunately all mine are at >10C as I use a DHT22 outside.
Any new ones I'll get from RS.