One of our systems I built as an interim setup until the big system goes online, was a 24v sealed Lead Carbon 300 AH bank, it had proven to be a tad small due to users piling on more and more loads, then leaving things running over night when not in use.
As the bulk charge voltage was almost 28v I decided to augment its capacity by paralleling it with a 24v 200AH bank of Lifepo4 cells re-purposed from dismantled 48v 100AH battery packs I had rescued. This has proven to be hugely successful, the Lifepo4 cells only get to 3.5V each, which is ideal, they do all the work, supplying power to the inverter until their voltage drops where the L.Carbon sealed cells take over.
I use one of those Kilovacs to isolate the Lifepo4 bank from the L.Carbon bank when their voltages start dropping near 22 volts, the BMS senses individual cell voltages and switches the bank out via the contactor, it re-enables it again when the Lead cell voltage > 24 volts.
So that is maybe another option, a new bank of 24v Lifepo4 cells will do all the heavy current grunt work, only drawing down on your older Lead as they start getting discharged. Here in NZ, Lifepo4 banks are less expensive than any form of lead.