Forum Index : Microcontroller and PC projects : Air monitor
Posted: 01:41pm
18 Jun 2026
This started off as an exploration of the BME688  and then turned into an air monitor by adding a Plantower PMS5003 particle matter sensor. The particulate information continuously scrolls across the bottom line. The code supports local pressure (QFE), sea level pressure adjusted assuming a standard atmosphere (QNH), and sea level pressure adjusted using the local temperature (QFF). This is configured in lines 31 and 35.
The code should also support the bme680 and bme690 (untested)
' AirMonitor.bas  -  combined air-quality monitor for the PicoMite:
'   * Bosch BME688/BME680  : temperature, pressure, humidity, gas + IAQ score
'   * Plantower PMS5003     : PM1.0 / PM2.5 / PM10 particulates
'   * 20x4 I2C character LCD: live display (PCF8574 backpack at &H27)
' PREREQUISITE (run once at the command prompt, NOT in this program):
'   OPTION SYSTEM I2C sdapin, sclpin
' The BME688 and the LCD both sit on that system I2C bus, so we neither set the
' pins nor open the port here.  The system I2C is on GP14/GP15 = channel 2, so
' the BME688 is accessed with the I2C2 READ/WRITE commands (no OPEN needed) and
' the LCD via I2CLCD, both talking to the system bus directly.
' Wiring
'   BME688 : VCC->3V3  GND->GND  SDA/SCL-> the system I2C pins   (3.3V part!)
'   LCD    : VCC->5V   GND->GND  SDA/SCL-> the same system I2C pins  (addr &H27)
'   PMS5003: VCC->5V(VBUS) GND->GND  TXD->GP1(COM1 RX)  RXD->GP0(COM1 TX)
'            SET->GP2 (high=run)     RST->GP3 (active-low reset)
OPTION EXPLICIT
OPTION DEFAULT NONE
' --- BME688 I2C address: 0x76 (SDO low) or 0x77 (SDO high) ------------------
CONST ADDR = &H76
CONST LCD_ADDR = &H27                  ' PCF8574 LCD backpack address
' --- your site altitude in metres above sea level --------------------------
' Used to report sea-level pressure instead of QFE (station pressure).
' Set to your actual height; 0 leaves the pressure as measured.
CONST ALTITUDE = 120
' Reduction method: 0 = QNH (ISA standard altimeter setting, temperature-
' independent); 1 = QFF (uses the live temperature, as many weather services
' report).  Both equal QFE when ALTITUDE = 0.
CONST USE_QFF = 1
' BME688 calibration coefficients (filled by ReadCalibration)
DIM FLOAT par_t1, par_t2, par_t3
DIM FLOAT par_p1, par_p2, par_p3, par_p4, par_p5, par_p6, par_p7, par_p8, par_p9, par_p10
DIM FLOAT par_h1, par_h2, par_h3, par_h4, par_h5, par_h6, par_h7
DIM FLOAT par_gh1, par_gh2, par_gh3
DIM FLOAT res_heat_range, res_heat_val, range_sw_err
DIM FLOAT t_fine                       ' carries temperature into P and H calc
DIM FLOAT amb_temp = 25                ' ambient for the heater target (updated each read)
DIM INTEGER variant                    ' 0 = BME680, 1 = BME688, 2 = BME690 (chip id 0x61 for all)
DIM INTEGER st                         ' gas status byte (reg 0x2D / 0x2B)
' BME680 (variant 0) gas-range lookup tables
DIM FLOAT k1(15) = (0,0,0,0,0,-1,0,-0.8,0,0,-0.2,-0.5,0,-1,0,0)
DIM FLOAT k2(15) = (0,0,0,0,0.1,0.7,0,-0.8,-0.1,0,0,0,0,0,0,0)
' --- IAQ scoring (open humidity+gas heuristic, NOT Bosch BSEC) --------------
CONST BURN_SECS  = 300                 ' warm-up seconds before showing IAQ
CONST HUM_BASE   = 40.0                ' ideal indoor relative humidity (%)
CONST HUM_WEIGHT = 0.25                ' humidity's share of the score
CONST BASE_UP    = 0.05                ' baseline rise rate toward cleaner air
CONST BASE_DECAY = 0.99999             ' slow baseline downward drift
DIM FLOAT gas_baseline = 0             ' rolling clean-air gas resistance reference
' --- PMS5003 particulate readings (kept between frames) --------------------
DIM INTEGER d(29)                      ' PMS frame bytes 2..31
DIM INTEGER pm1, pm25, pm10            ' last good PM1.0 / PM2.5 / PM10 (ug/m3)
DIM INTEGER c03, c05, c10, c25, c50, c100  ' particle counts per 0.1L (>0.3 .. >10um)
' --- pressure trend arrow: based on the change over (up to) the last 3 hours.
'     One arrow = a normal move, a double arrow = changing fast. --------------
CONST NHIST       = 180                ' pressure history slots
CONST P_SAMPLE_MS = 60000              ' one sample per minute -> 180 slots = 3 hours
CONST P_STEADY    = 0.7                ' |3h change| below this (hPa) shows steady (=)
CONST P_FAST      = 1.6                ' |3h change| at/above this (hPa) shows a double arrow
DIM FLOAT phist(NHIST - 1)             ' circular pressure history (hPa)
DIM INTEGER pwi = 0, pn = 0            ' ring write index, count of valid samples
' LCD custom-character codes (0 = degree, auto-created by I2CLCD INIT)
CONST CH_UP = 1, CH_DN = 2, CH_EQ = 3  ' rising / falling / steady arrows
' --- display timing --------------------------------------------------------
CONST MEAS_MS   = 3000                 ' how often to take a full sensor measurement
CONST SCROLL_MS = 250                  ' marquee step interval (line 4)
' Start up
I2CLCD INIT LCD_ADDR                    ' uses the system I2C bus
I2CLCD CLEAR
I2CLCD BACKLIGHT 1
I2CLCD CREATECHAR CH_UP, &H04,&H0E,&H15,&H04,&H04,&H04,&H04,&H00   ' rising arrow
I2CLCD CREATECHAR CH_DN, &H04,&H04,&H04,&H04,&H15,&H0E,&H04,&H00   ' falling arrow
I2CLCD CREATECHAR CH_EQ, &H00,&H00,&H1F,&H00,&H1F,&H00,&H00,&H00   ' steady (=)
LcdLine 1, "Air monitor"
LcdLine 2, "starting..."
WB(&HE0, &HB6)                          ' BME688 soft reset (clears heater control)
PAUSE 10
IF RB%(&HD0) <> &H61 THEN
 PRINT "No BME688/BME680 at &H"; HEX$(ADDR); " - chip id &H"; HEX$(RB%(&HD0))
 LcdLine 1, "BME688 not found"
 LcdLine 2, "id &H" + HEX$(RB%(&HD0), 2)
 END
ENDIF
variant = RB%(&HF0)                     ' 0 = BME680, 1 = BME688
ReadCalibration
' PMS5003 on COM1
SETPIN GP1, GP0, COM1                   ' rx=GP1, tx=GP0
OPEN "COM1:9600, 256" AS #1
SETPIN GP2, DOUT                        ' SET   : high = run
SETPIN GP3, DOUT                        ' RESET : active low
PIN(GP2) = 1
PIN(GP3) = 0 : PAUSE 20 : PIN(GP3) = 1  ' pulse reset, then release
PAUSE 100
' Main loop: lines 1-3 are a fixed at-a-glance summary, line 4 scrolls the PM
' readout.  Sensors are read every MEAS_MS; line 4 scrolls on an absolute
' timebase (nextscroll) so its cadence stays even between reads.
DIM INTEGER t0 = TIMER
DIM INTEGER burning = 1, measuring = 0
DIM INTEGER nextmeas = 0, nextpsample = 0, nextscroll = 0, scrollpos = 0
DIM INTEGER secsleft, idx
DIM FLOAT tC, pHPa, slp, rh, gasR, iaq, slowref   ' slp = sea-level pressure (QNH or QFF)
DIM STRING l3, marquee, plabel
marquee = "Starting up...      "
IF USE_QFF THEN plabel = "QFF " ELSE plabel = "QNH "
DO
 ' --- BME688: trigger a measurement when due, collect it when the chip is
 '     ready.  Splitting it this way keeps the ~150ms conversion from blocking
 '     the scroll.  measuring/new_data are tested in NESTED IFs (never ANDed)
 '     because MMBasic AND is bitwise - "measuring AND (st AND &H80)" would be
 '     1 AND 128 = 0 and the read would never happen. ------------------------
 IF measuring THEN
   IF (RB%(&H1D) AND &H80) THEN         ' new_data set -> read the result
     tC   = ReadTemperature()
     pHPa = ReadPressure() / 100.0                 ' QFE (station pressure)
     IF USE_QFF THEN                               ' reduce QFE to sea level
       slp = pHPa * EXP(ALTITUDE * 9.80665 / (287.05 * (tC + 273.15)))   ' QFF (live temp)
     ELSE
       slp = pHPa / (1 - ALTITUDE / 44330.0) ^ 5.255                     ' QNH (ISA standard)
     ENDIF
     rh   = ReadHumidity()
     IF variant >= 1 THEN st = RB%(&H2D) ELSE st = RB%(&H2B)  ' 688/690 gas_lsb 0x2D, 680 0x2B
     IF (st AND &H20) THEN gasR = ReadGas() ELSE gasR = -1
     ' rolling gas baseline - adapt only on valid, heater-stable readings
     IF gasR >= 0 THEN
       IF (st AND &H10) THEN
         IF gas_baseline = 0 THEN
           gas_baseline = gasR
         ELSEIF gasR > gas_baseline THEN
           gas_baseline = gas_baseline + BASE_UP * (gasR - gas_baseline)
         ELSE
           gas_baseline = gas_baseline * BASE_DECAY
         ENDIF
       ENDIF
     ENDIF
     secsleft = INT((BURN_SECS * 1000 - (TIMER - t0)) / 1000)
     IF secsleft <= 0 THEN burning = 0
     PollPMS                            ' parse whatever PMS frames have arrived
     ' air-quality text for line 3
     IF gasR < 0 THEN
       l3 = "IAQ --"
     ELSEIF burning THEN
       l3 = "Warmup " + STR$(secsleft) + "s"
     ELSE
       iaq = AirQuality(gasR, rh)
       l3  = "IAQ" + STR$(iaq, 0, 0) + " " + AirLabel$(iaq)
     ENDIF
     ' sea-level pressure change over (up to) the last 3 hours
     IF pn > 0 THEN
       idx = (pwi - pn + NHIST) MOD NHIST : slowref = phist(idx)   ' oldest (<=3h) sample
     ELSE
       slowref = slp
     ENDIF
     ' fixed summary lines (one arrow = moving, two arrows = moving fast)
     LcdLine 1, "Temp " + STR$(tC, 0, 1) + CHR$(0) + "C   RH " + STR$(rh, 0, 0) + "%"
     LcdLine 2, plabel + STR$(slp, 0, 1) + "hPa " + Trend$(slp - slowref)
     LcdLine 3, l3
     ' PM values + per-size particle counts for the scrolling line
     marquee = "PM1.0 " + STR$(pm1) + " ug/m3    "
     marquee = marquee + "PM2.5 " + STR$(pm25) + " ug/m3    "
     marquee = marquee + "PM10 " + STR$(pm10) + " ug/m3    "
     marquee = marquee + "Counts per 0.1L  "
     marquee = marquee + ">0.3um " + STR$(c03) + "  >0.5um " + STR$(c05) + "  >1.0um " + STR$(c10) + "  "
     marquee = marquee + ">2.5um " + STR$(c25) + "  >5.0um " + STR$(c50) + "  >10um " + STR$(c100) + "        "
     measuring = 0
     nextmeas = TIMER + MEAS_MS
   ENDIF
 ELSEIF TIMER >= nextmeas THEN
   TriggerMeasure                       ' start a forced conversion (returns immediately)
   measuring = 1
 ENDIF
 ' --- sample the sea-level pressure history once a minute ---
 IF TIMER >= nextpsample AND pHPa > 0 THEN
   phist(pwi) = slp
   pwi = (pwi + 1) MOD NHIST
   IF pn < NHIST THEN pn = pn + 1
   nextpsample = TIMER + P_SAMPLE_MS
 ENDIF
 ' --- scroll line 4 on an absolute, self-correcting cadence ---
 IF TIMER >= nextscroll THEN
   LcdLine 4, Marq$(marquee, scrollpos, 20)
   scrollpos = scrollpos + 1
   IF scrollpos >= LEN(marquee) THEN scrollpos = 0
   nextscroll = nextscroll + SCROLL_MS
   IF nextscroll < TIMER THEN nextscroll = TIMER + SCROLL_MS   ' resync after the measurement stall
 ENDIF
 PAUSE 2                                ' small pause so nextscroll is checked promptly
LOOP
' LCD helper: write text left-justified on a line, padded/truncated to 20 cols
SUB LcdLine(ln%, t$)
 I2CLCD ln%, 1, LEFT$(t$ + SPACE$(20), 20)
END SUB
' Return a w-char window of s$ starting at pos, wrapping around (for the marquee).
' Builds at most w chars, so it never exceeds the 255-char string limit.
' (Named Marq$ not Scroll$ - SCROLL is a reserved MMBasic command keyword.)
FUNCTION Marq$(s$, p0%, nch%)
 LOCAL INTEGER n, p
 n = LEN(s$)
 p = p0% MOD n
 IF p + nch% <= n THEN
   Marq$ = MID$(s$, p + 1, nch%)
 ELSE
   Marq$ = MID$(s$, p + 1, n - p) + MID$(s$, 1, nch% - (n - p))
 ENDIF
END FUNCTION
' Arrow(s) for a pressure change 'delta' (hPa over ~3h):
'   below P_STEADY     -> "="   steady
'   P_STEADY..P_FAST   -> one arrow   (rising / falling)
'   >= P_FAST          -> two arrows  (rising / falling fast)
FUNCTION Trend$(delta AS FLOAT)
 IF delta >= P_FAST THEN
   Trend$ = CHR$(CH_UP) + CHR$(CH_UP)
 ELSEIF delta >= P_STEADY THEN
 ELSEIF delta <= -P_FAST THEN
   Trend$ = CHR$(CH_DN) + CHR$(CH_DN)
 ELSEIF delta <= -P_STEADY THEN
 ELSE
   Trend$ = CHR$(CH_EQ)
 ENDIF
END FUNCTION
' PMS5003 serial helpers (non-blocking)
' Parse any complete frames already in the COM1 buffer, keeping the latest.
' Never waits, so the scrolling display stays smooth.
SUB PollPMS
 LOCAL INTEGER c, i, sum, chk
 DO WHILE LOC(#1) >= 32                  ' only start when a full frame is buffered
   c = GetByteNB%()
   IF c = &H42 THEN
     c = GetByteNB%()
     IF c = &H4D THEN
       sum = &H42 + &H4D
       FOR i = 0 TO 29
         c = GetByteNB%()
         IF c < 0 THEN EXIT SUB           ' ran dry mid-frame (rare); bail out
         d(i) = c
         IF i < 28 THEN sum = sum + c
       NEXT i
       chk = (d(28) << 8) OR d(29)
       IF chk = sum THEN
         pm1 = BE16%(d(), 8) : pm25 = BE16%(d(), 10) : pm10 = BE16%(d(), 12)
         c03  = BE16%(d(), 14) : c05  = BE16%(d(), 16) : c10  = BE16%(d(), 18)
         c25  = BE16%(d(), 20) : c50  = BE16%(d(), 22) : c100 = BE16%(d(), 24)
       ENDIF
     ENDIF
   ENDIF
 LOOP
END SUB
' Read one byte from COM1, or -1 if the buffer is empty (no waiting)
FUNCTION GetByteNB%()
 LOCAL STRING s
 s = INPUT$(1, #1)
 IF s = "" THEN GetByteNB% = -1 ELSE GetByteNB% = ASC(s)
END FUNCTION
' Combine two big-endian PMS frame bytes into a 16-bit value
FUNCTION BE16%(d%(), hi%)
 BE16% = (d%(hi%) << 8) OR d%(hi% + 1)
END FUNCTION
' BME688 low-level I2C helpers (system I2C bus - no OPEN needed)
FUNCTION RB%(reg%)
 LOCAL INTEGER b
 I2C2 WRITE ADDR, 1, 1, reg%            ' option 1 = keep the bus (repeated start)
 I2C2 READ ADDR, 0, 1, b
 RB% = b
END FUNCTION
SUB WB(reg%, val%)
 I2C2 WRITE ADDR, 0, 2, reg%, val%
END SUB
FUNCTION S8(v%) AS FLOAT
 IF v% > 127 THEN S8 = v% - 256 ELSE S8 = v%
END FUNCTION
FUNCTION S16(v%) AS FLOAT
 IF v% > 32767 THEN S16 = v% - 65536 ELSE S16 = v%
END FUNCTION
' BME688 calibration, measurement and compensation
SUB ReadCalibration
 par_t1  = (RB%(&HEA) << 8) OR RB%(&HE9)
 par_t2  = S16((RB%(&H8B) << 8) OR RB%(&H8A))
 par_t3  = S8(RB%(&H8C))
 par_p1  = (RB%(&H8F) << 8) OR RB%(&H8E)
 par_p2  = S16((RB%(&H91) << 8) OR RB%(&H90))
 par_p3  = S8(RB%(&H92))
 par_p4  = S16((RB%(&H95) << 8) OR RB%(&H94))
 par_p5  = S16((RB%(&H97) << 8) OR RB%(&H96))
 par_p6  = S8(RB%(&H99))
 par_p7  = S8(RB%(&H98))
 par_p8  = S16((RB%(&H9D) << 8) OR RB%(&H9C))
 par_p9  = S16((RB%(&H9F) << 8) OR RB%(&H9E))
 par_p10 = RB%(&HA0)
 par_h1  = (RB%(&HE3) << 4) OR (RB%(&HE2) AND &H0F)
 par_h2  = (RB%(&HE1) << 4) OR (RB%(&HE2) >> 4)
 par_h3  = S8(RB%(&HE4))
 par_h4  = S8(RB%(&HE5))
 par_h5  = S8(RB%(&HE6))
 par_h6  = RB%(&HE7)
 par_h7  = S8(RB%(&HE8))
 par_gh1 = S8(RB%(&HED))
 par_gh2 = S16((RB%(&HEC) << 8) OR RB%(&HEB))
 par_gh3 = S8(RB%(&HEE))
 res_heat_range = (RB%(&H02) AND &H30) >> 4
 res_heat_val   = S8(RB%(&H00))
 range_sw_err   = S8(RB%(&H04) AND &HF0) / 16.0
END SUB
' Start one forced-mode measurement and return immediately (non-blocking).
' The main loop polls status reg 0x1D bit7 (new_data) and reads the result
' when it is set, so the ~150ms conversion does not stall the scroll.
SUB TriggerMeasure
 WB(&H72, &H01)                         ' ctrl_hum: osrs_h = 1
 WB(&H5A, ResHeat(300, amb_temp))       ' res_heat_0 (target 300C)
 WB(&H64, &H65)                         ' gas_wait_0: ~148 ms
   WB(&H71, &H20)                       ' run_gas bit 5 (BME688/BME690)
 ELSE
   WB(&H71, &H10)                       ' run_gas bit 4 (BME680)
 ENDIF
 WB(&H70, &H00)                         ' heater on
 WB(&H74, (2 << 5) OR (5 << 2) OR 1)    ' osrs_t x2, osrs_p x16, forced mode -> start
END SUB
FUNCTION ReadTemperature() AS FLOAT
 LOCAL INTEGER raw
 LOCAL FLOAT v1, v2
 raw = (RB%(&H22) << 12) OR (RB%(&H23) << 4) OR (RB%(&H24) >> 4)
 v1 = (raw / 16384.0 - par_t1 / 1024.0) * par_t2
 v2 = ((raw / 131072.0 - par_t1 / 8192.0) * (raw / 131072.0 - par_t1 / 8192.0)) * par_t3 * 16.0
 t_fine = v1 + v2
 amb_temp = t_fine / 5120.0
 ReadTemperature = amb_temp
END FUNCTION
FUNCTION ReadPressure() AS FLOAT
 LOCAL INTEGER raw
 LOCAL FLOAT v1, v2, v3, p
 raw = (RB%(&H1F) << 12) OR (RB%(&H20) << 4) OR (RB%(&H21) >> 4)
 v1 = (t_fine / 2.0) - 64000.0
 v2 = v1 * v1 * (par_p6 / 131072.0)
 v2 = v2 + (v1 * par_p5 * 2.0)
 v2 = (v2 / 4.0) + (par_p4 * 65536.0)
 v1 = (((par_p3 * v1 * v1) / 16384.0) + (par_p2 * v1)) / 524288.0
 v1 = (1.0 + (v1 / 32768.0)) * par_p1
 IF v1 = 0 THEN ReadPressure = 0 : EXIT FUNCTION
 p = 1048576.0 - raw
 p = ((p - (v2 / 4096.0)) * 6250.0) / v1
 v1 = (par_p9 * p * p) / 2147483648.0
 v2 = p * (par_p8 / 32768.0)
 v3 = (p / 256.0) * (p / 256.0) * (p / 256.0) * (par_p10 / 131072.0)
 ReadPressure = p + (v1 + v2 + v3 + (par_p7 * 128.0)) / 16.0
END FUNCTION
FUNCTION ReadHumidity() AS FLOAT
 LOCAL INTEGER raw
 LOCAL FLOAT temp, v1, v2, v3, v4, h
 raw = (RB%(&H25) << 8) OR RB%(&H26)
 v1 = raw - ((par_h1 * 16.0) + ((par_h3 / 2.0) * temp))
 v2 = v1 * ((par_h2 / 262144.0) * (1.0 + ((par_h4 / 16384.0) * temp) + ((par_h5 / 1048576.0) * temp * temp)))
 v3 = par_h6 / 16384.0
 v4 = par_h7 / 2097152.0
 h = v2 + ((v3 + (v4 * temp)) * v2 * v2)
 IF h > 100.0 THEN h = 100.0
 IF h < 0.0 THEN h = 0.0
 ReadHumidity = h
END FUNCTION
' Gas resistance in Ohms.  BME688/BME690 result is at 0x2C/0x2D, BME680 at 0x2A/0x2B.
FUNCTION ReadGas() AS FLOAT
 LOCAL INTEGER raw, rng, msb, lsb
   msb = RB%(&H2C) : lsb = RB%(&H2D)
   raw = (msb << 2) OR (lsb >> 6) : rng = lsb AND &H0F
   ReadGas = GasHigh(raw, rng)
 ELSE
   msb = RB%(&H2A) : lsb = RB%(&H2B)
   ReadGas = GasLow(raw, rng)
 ENDIF
END FUNCTION
FUNCTION GasHigh(raw%, rng%) AS FLOAT
 LOCAL INTEGER v1, v2
 v1 = &H40000 >> rng%
 v2 = 4096 + ((raw% - 512) * 3)
 GasHigh = 1000000.0 * v1 / v2
END FUNCTION
FUNCTION GasLow(raw%, rng%) AS FLOAT
 LOCAL FLOAT var1, var2, var3, grange
 grange = 1 << rng%
 var1 = 1340.0 + (5.0 * range_sw_err)
 var2 = var1 * (1.0 + k1(rng%) / 100.0)
 var3 = 1.0 + (k2(rng%) / 100.0)
 GasLow = 1.0 / (var3 * 0.000000125 * grange * (((raw% - 512.0) / var2) + 1.0))
END FUNCTION
' IAQ score 0-100 (higher = cleaner) from gas resistance and humidity
FUNCTION AirQuality(g AS FLOAT, h AS FLOAT) AS FLOAT
 LOCAL FLOAT hum_offset, hum_score, gas_score
 hum_offset = h - HUM_BASE
 IF hum_offset > 0 THEN
   hum_score = (100.0 - HUM_BASE - hum_offset) / (100.0 - HUM_BASE) * (HUM_WEIGHT * 100.0)
 ELSE
   hum_score = (HUM_BASE + hum_offset) / HUM_BASE * (HUM_WEIGHT * 100.0)
 ENDIF
 IF g < gas_baseline THEN
   gas_score = (g / gas_baseline) * (100.0 - HUM_WEIGHT * 100.0)
 ELSE
   gas_score = 100.0 - HUM_WEIGHT * 100.0
 ENDIF
 AirQuality = hum_score + gas_score
END FUNCTION
FUNCTION AirLabel$(s AS FLOAT)
 IF s >= 90 THEN
   AirLabel$ = "excellent"
 ELSEIF s >= 70 THEN
   AirLabel$ = "good"
 ELSEIF s >= 50 THEN
   AirLabel$ = "fair"
 ELSEIF s >= 30 THEN
   AirLabel$ = "poor"
 ELSE
   AirLabel$ = "bad"
 ENDIF
END FUNCTION
FUNCTION ResHeat(target%, amb%) AS FLOAT
 LOCAL FLOAT t, v1, v2, v3, v4, v5
 t = target%
 IF t > 400 THEN t = 400
 v1 = (par_gh1 / 16.0) + 49.0
 v2 = ((par_gh2 / 32768.0) * 0.0005) + 0.00235
 v3 = par_gh3 / 1024.0
 v4 = v1 * (1.0 + (v2 * t))
 v5 = v4 + (v3 * amb%)
 ResHeat = INT(3.4 * ((v5 * (4.0 / (4.0 + res_heat_range)) * (1.0 / (1.0 + (res_heat_val * 0.002)))) - 25))
END FUNCTION
Edited 2026-06-19 00:19 by matherp