tinyt
Guru

  Bryan1 said  Ok this time I put the clamp meter close to the negative battery terminal, turned on the toaster oven and one element.

Now 23.51 x 101.2 = 2379.2

The energy meter 2372.3 so that a lot better, now the AC voltage was 235 volts and I did notice turning on a 2nd element caused the voltage to drop to 215 volts.


Efficiency = 100 X (2372.3 / 2379.2) = 99.7% WOW!!

This is an inverter manufacturer's and DIY'ers dream!!
 
Posted: 09:57pm
12 Apr 2026
Copy link to clipboard
Bryan1
Guru


With Phill's suggest of switching noise causing a higher amperage moving the clamp meter to close to the Vbat ground was the best move so a true reading could be taken.

Once again a huge Thank You to all the members that have helped me with this project and I am just glad it's finished and working.

Regards Bryan
 
Posted: 11:23pm
12 Apr 2026
Copy link to clipboard
Bryan1
Guru


Thought to take a measurement with just the shed load going.

VBat 28.7
VBat current 34.2
Energy meter Watts 101 average

So 100 x (981.5/101) = 97.1%



Just got a text that Ali inverter is here too
 
Posted: 12:02am
13 Apr 2026
Copy link to clipboard
Bryan1
Guru


Ok this Ali board is here  




On the left is the blue one I'm going to use as it is the upgraded board.

Now as all the outputs are in Chinese could a member please tell me what each connection is as we do need to know what each one is.

Regards Bryan
 
Posted: 12:39am
13 Apr 2026
Copy link to clipboard
Bryan1
Guru


Now I do have that first small inverter to use for this inverter for testing  

The choke uses the big choke from the AeroSharp Grid Tie with 10 turns of 6.5x3.5 enameled wire then varnished in. It would be good to set this choke with a scope to see what it can make as dual choke.

I got this design off Tony many years ago now when I tested this inverter it did run both vacuums  




There is no pre start setup for this small inverter and it didn't blowup but now I know more a pre start setup will be done.
 
Posted: 01:46am
13 Apr 2026
Copy link to clipboard
Godoh
Guru

Hi Bryan, the connections can take a while to work out.
Near the transformer one of the sockets is for feedback, so if you have a look at which socket goes straight to the transformer that should be the feedback one.
Another one is for the LED to show the inverters state, either On or Standby.

The next set of sockets to the left will have one for the fan.

I will take some photos of my board and see if it is the same as yours.
Unfortunately they are a few different boards with different arrangements for the sockets.
If you can contact the seller of the board they can usually supply a diagram to show how the connections are made.

I will post a picture of my inverter later

Pete
 
Posted: 02:33am
13 Apr 2026
Copy link to clipboard
Bryan1
Guru


Hi Pete I may of answered most of my questions myself as I do have the picture from that small inverter board  




Now it shows the top connection at the top of the group is for the fan output, now on this larger inverter at the back of this board is a 12 volt connector. I do assume this would be to connect a fan to the heatsink so I'm wondering if this larger board does have a 2 fan setup.

Also below the 2 trim pots is a 2 pin connector that goes to that vertical board so wouldn't this be a 12 or 15 volt DC input.
 
Posted: 04:07am
13 Apr 2026
Copy link to clipboard
Godoh
Guru

Hi Bryan I see on the larger board that there is an extra connector near the small board on the opposite side of the transformer on the board.
One way to translate the symbols may be to take photos and use a translation program to translate from chinese to english.
None of my boards have that small vertical board
Pete
 
Posted: 08:19am
13 Apr 2026
Copy link to clipboard
Godoh
Guru



Hi Bryan this is the connection diagram for the board I have

Pete
 
Posted: 12:35pm
13 Apr 2026
Copy link to clipboard
tinyt
Guru

  Bryan1 said  Thought to take a measurement with just the shed load going.

VBat 28.7
VBat current 34.2
Energy meter Watts 101 average

So 100 x (981.5/101) = 97.1%



Just got a text that Ali inverter is here too


Efficiency = 100 x (Watts Output / Watts Input) = 100 x (Energy meter reading / (Vbat x Bat Current)
Efficiency =  100 x (101/(28.7 * 34.2)) = 100 x (101/981.54) = 10.29% ???
 
Posted: 03:25am
30 May 2026
Copy link to clipboard
Bryan1
Guru


Well decided to give my chainsaws a good clean so when I decided to turn on my air compressor thought I have a look at the surge current on the energy meter.

20Kw   was the draw and the inverter just handled it now it's just clicked over 82Kwh and still going strong.

Regards Bryan
 
Posted: 04:27am
30 May 2026
Copy link to clipboard
phil99
Guru


Perhaps your energy meter is unable to correct for power factor during a surge.
20kVA looks about right for a compressor motor starting, but it's P.F. during starting is probably around 0.3 so that would be 20 x .3 = 6kW. Still quite respectable.
 